Which ciass CT can be use in diff. protection. Can be use
5p20?
Answers were Sorted based on User's Feedback
Conventionally only PS class CT shall be used for unit
protections. But now a days, with the use of miro processor
based relays having facility of low impedance or biased
differential protection, 5P20 may be used as biasing in the
relay takes care of the unmatched characteristics of the
both side Cts.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / avdhesh
Class 5p20 CT is a protection class CT which is used for
normal protections. For differential protection you must
use class PS CT.
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / persistence
yes 5P20 class CT can be used for differential
protection,In our industry they have been used for
transformer differential protection,transformer being 10 mva
and for bus differential protn. class PS has been used.
| Is This Answer Correct ? | 10 Yes | 5 No |
Answer / dharmaraj
For diff.protn you must use ps(or) px class CT.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / dheena hitech
For diff protection we should be use PS or PX class Because
of yjat one ine is spl. class for diff and Dist protection
| Is This Answer Correct ? | 1 Yes | 2 No |
why anti pumping relay is not given to tripping coil of the breaker? why only to closing coil?
What is current divider rule (cdr)?
What is signal flow graph?
transmission line losses
Brief use of isolation transformer & how it works.
we have 400kv/6.6kv transformer ,it has total 9 taps on HV side with normal tap on tap no 5.when we took the ratio test we observed that ratio was decreasing from tap 1 to tap 5 and was found increasing from tap 5 to tap 9.What is the reason?if anyone have related document then please send me on the email id ankushbahale@gmail.com......plz plz
What is the Working principle of ELCB and RCCB?
why dc is used in control circuits for MV & LV switchgeras instead of ac
ASTM D 3455 - Standard Test Methods for Compatibility of Construction Material with Electrical Insulating Oil of Petroleum Origin has been used for Testing Transformer Oils with a product placed in it. Aged Control Oil has a Power Factor of 0.032% at 100°C. Aged Oil with a Test component has a Power Factor of 0.093% at 100°. Is this increase acceptable? If not why? How much increase is acceptable?
why the protection turbo generators is most complex?
Why AC current leads voltage in capacitor and how?
Is your generator is automated or manual if so do you know the circuits?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)