Is your generator is automated or manual if so do you know
the circuits?
Answers were Sorted based on User's Feedback
Answer / yuvi
Honestly, this question does not make any sense. However, I
will try to answer to the best of my understanding.
1) I don’t have a generator.
2) Difference between manual and automated generator is
that in a manual start generator, we will have to manually
start it. In an automatic start generator, a circuit senses
that the power has failed and starts the generator
automatically using a small battery powered motor similar
to the ones that start your car. The sensing circuit can be
of a wide variety. It can be a magnetic relay or an
electronic circuit depending on the area of application.
Is This Answer Correct ? | 14 Yes | 1 No |
Answer / tapas
in both Auto and Manual cases circuit diagram can be found in the Drawing of Sync panel/AMF panel. Its a selector switch by which user can select either Auto mode or Manual mode.
DG start and stop circuit has two ways to operate which can be found on drawing.
1.Manual Mode: In this mode push button start and push button stop operates DG. i.e. when power fails DG can't be started Automatically. Operator should start the DG manually.
2. Automode: PLC senses absence of Power and commands DG to start.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / ferozuddin
generator wiil be function as a manual and also auto .
manual in case of when there will be no interface with the
auto transfer switch (ATS).when generator is interface with
the ATS it will work auto in case of emergency
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / mani0786
mannully start genset start manually & wwhen it come with a amf or ats panel it said auto genset well sir your question is out my mind but so i give it a simple sot
Is This Answer Correct ? | 1 Yes | 0 No |
we have 3 types
1.manual
2..auto.3.semi manual
Is This Answer Correct ? | 0 Yes | 0 No |
Its very simple
Take an 230v auxillary contactor with 1NO POINT and 1NC POINT
One single phase connect at one side NO POINT and other end connect to contactor A1(NO VOLT COIL).A2NEUTRAL directly connected.
Positive (+) supply24 v connected at NC POINT one side and other end connected at generator starting switch .
When EB powersupply is there the contactor is on.
When EB supply cut through NC POINT the positive supply passing to the switch so the generator is on.
Its very cheap.
Is This Answer Correct ? | 0 Yes | 1 No |
We have three 33kv substations. All of them energised by same source.When i am checking the phase sequence between one substation to other substation (like R Phase to R Phase) by multimeter i am getting some voltage.Near to LT panels UPS panels are there. Can u explain whether any possible to happen like that. In Phase SEquencemeter is showing correctly in both substations. How is it happen. Explain me.Explain me communication signal will produce Phase difference on this case.
relation between voltage and frequency.
5 Answers IIUI, Lucky Cement, Reliance,
what is the difference between neutral and earth
In EDO ACBs what is a purpose of closing coil and motor, what is the operation of these devices are they inetconnected. means if we give supply to motor and by BCS we charge Closing coil,what exact is operation is and how it charge a spring of ACB. Sir if anybody has an wiring diagram please send me the link to operate and EDO breaker.
how to find insulation resistance of a generator(11kv) by theoritical formula??
Off-circuit Tap changers in distribution transformer required
in 3phase 50kva dg what is the full load current for single phase laod
Why there is no provision of breaker in between primary of UAT and generator
What is the different between digital phase converter and ordinary phase converter?
what is level 2 automation?
what is function of rtu?
Why thwe Direction of Rotation of a TABLE Fan & CEILING Fan are different?