Answer / vinodh.t,sil,bellary
class-a
1.differential
2.over fluxing
3.residual over voltage
4.field failure
5.startup current
6.100% earth fault
7.low forward
claa-b
turbine trip+low forward
class-c
1.0ver frequency
2.under frequency
3.negative phase sequence
4.thermal over load
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / v_ram
hi vinodh....
is there any class-d trip in generator?
Is This Answer Correct ? | 2 Yes | 1 No |
State the factors, for the choice of electrical system for an aero turbine.
Fire pumps are not used with ELCB control, why ?
why various test are performed on electrical panels & power cables before commissioning on site & what are these test???
How CT is connected to measure current by changing plug setting , ratio is 300 - 150 / 5 A ?
1 Answers Ajanta Pharma, Bhel, Cosmo Films, Suzlon,
wath is skin effect?
some ac motor's direction get change dueto ghanging input to the ac drives.(say ryb to rby). but some motor direction remains the same when phase sequence is changed fromdive side. can anybody guide me?
Pls Breifly explain about UPS (Inverter,Reserve,Rectifier,Float voltage,Boost voltage).
What is the formula to calculate distribution transformer De-rating on iron losses basis
1.what is difference in maintain Hz again Hz in USA ? 2.how to calculate the battery AH? 3.why are yearly maintained in transformer how many tests in required?
how to measure dc earth leakage current?
What is the Impedance, inductive reactance calculations
How to calculate the phase to phase clearness of HT /// LT bus bar?????