Getting nusense tripping in a 11KV soft starter, have
checked all it control supply & contactors but did not get
any fault please help.
Answers were Sorted based on User's Feedback
Answer / arun
Check your load.Check the relay settings and current
measured during starting.
Check winding resistances in each phase,earthings,IR values
of the motor.
Run the motor without load for sometime if possible monitor
the current in each phase.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / neeraj katoch
check the motor on no load , check the winding of motor and
check the cantrol panel of motor may be realy upset.
Is This Answer Correct ? | 0 Yes | 0 No |
An engineer measures the direct current resistance of a transformer using ohm meter. When he/she takes out one of the leads of the meter, spark comes.. Why ?? This effect is known as...
Why A.C. capacity given in Ton. Ex. - 1.5 Ton
from where the self excitrd induction generator get the power?why is the voltage regulation is poor of seig?
Which is stiffer between salient pole rotor and cylindrical rotor synchronous machines? Justify your answer.
what is DRP panels?
please tell me the all the spcications of the 100MW 11KV HYDEL POWER PLANT SPECICATIONS
What Happen When We provide Dc Supply to Ac Motor
Is a contactor (or master relay) required between incoming lines and a VFD? The question goes to safety. If a contactor were used before the VFD and an e-stop engaged then the motor will coast to a stop (i.e. VFD loses power) instead of stopping much faster if the VFD braking fucntion were used. It would make more sense to keep power on the VFD.
In a 11Kv/433Volt Delt-star step down transformer one one line(Line-B) of HT site is open & earthed on DP structur. What will be the voltage on LT side R-Y, Y-B,B-R and R-N, Y- N & B-N?. Please help to understand the problem with examples. Arvind , Jaipur.
Anyone who can recommend an equivalent to Envirotemp FR3 of Cooper?
what will happen if ac and dc supplies given
What is trickle charging system?