what is the basic differnce between ground and earth
Answers were Sorted based on User's Feedback
As mentioned earth and ground are the same terms used in
different countries. The earth (ground) conductor is
electrically connected to the earth so that anything it is
connected to, cannot become live. There will be be some kind
of local regulation determining the maximum resistance that
is allowed where the connection is made to ground (rod, mat etc)
The neutral is one connection of the supply transformer that
is also connected to earth. It is not a return path as such
because ac is changing direction. The reason it is connected
to earth is for safety. It means that a fault (to earth) of
the live conductor will cause the overcurrent device (fuse
or breaker) to operate and trip the power.
There are systems that do not connect one side of the supply
transformer to earth (no neutral). They still function just
the same as an earthed system. This is more common in
military or medical and requires some form of sensing
circuit to detect faults but the fault gives an alarm rather
than a trip so that power remains until an outage can be
planned to find the fault.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / gopi
GROUND AND EARTH ARE EQUIVALENT BUT EQUAL,
GROUND-FLUCTUATION OF LOAD IN OUTSIDE,THE IMBALANCE CURRENT
IS FLOWING ,THIS IMBALANCE CURRENT NUTRALISE BY GROUND.
EARTH- IT NUTRALISE THE EXCESS AMOUNT OF CURRENT WHEN
APPLIANCE BECOME SHORT CKT.
| Is This Answer Correct ? | 0 Yes | 0 No |
Earth means always earth , ground may be earth or large conducting body as in vehicles,ships ..
| Is This Answer Correct ? | 0 Yes | 0 No |
1.what is the funtion of chiller primary & scondary pumps. 2.what is the use of distribution lines & Types. 3.what is the use the thermal power stations & how much capacity.
what is difference between power transformer and distribution transformers
Enlist four components of electrive drives.
types of arc quenching methodes
How Size of Busbar is determined for a particular load.
how to calculate cooling requirement of datacentre from electrical load?
at work we have a 3 phase motor but on testing one phase isnt getting a reading. it runs 24 hours a day all week. stops and starts well no noise or heating. the phase isnt down to earth.is it just a bad meter reading or not? phases one and three came up with a resistance reading of 0.4 but phase 2 couldnt get anything shows up as open circuit.
which is better ac or dc?
what is the instrument used for measuring insulator RESISTANCE
what type of questions are asked and howmwny questions belong this catagory?
How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?
What is transmittance?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)