WHAT IS THE USE OF ANTIPUMPING CONTACTOR IN HT BREAKERS
Answers were Sorted based on User's Feedback
Answer / felix
its nothing but an interlock for repetitive open/close
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / suresh chand
The main purpose of anpumping relay is to protect Circuit breaker in fault condition when CB is receiving direct closing command.
if a circuit breaker is reciving direct closing command or there is any shorting in its closing circuit and simultaniously there is in fault then the CB then the will close and trip many times and will damage its pole. by proving antipumping contactor/relay the VCB will not close electrical again untill closing pulse is removed. It contact also comes in series with closing circuit hence also act as a interlock in closing circuit.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / rahul sharma
antipumping is a term itself sowing that prevention of
pumping . in antipumping when breaker had all ready closed
it will prevent to get other closing comand to coill. so
coill prevent from damage .
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / p dinesh
It is for the prevention of closure of breaker at faulty
condition
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / vinodg
Antipumping is preventing the continuos close/trip of
Circuit Breaker with single command during fault or
interlock trip exist.
ie Circuit breaker will close only once when trip signal
exist.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / s.gowrisankar
MR.FELIX i say that it is only the interlock for
closing,opening won't come in to picture
Is This Answer Correct ? | 0 Yes | 4 No |
what is a lightning arrester???
How can a transformer test by megger?
What is Surge Capacitor? Why it is require in Generator Circuit Breaker,inspite of surge arrester?
what is derating factor in Cable ? how we minimise this?
18 Answers Bhel, College School Exams Tests,
What are insulation classes? Tell examples of each of them.
how to calculate the ac and dc wire losses with calculations plz tell me
Approach of a cooling tower is the difference between temperatures of what factors?
dear all, can any body explain that how to select an induction motor for a specific mechanical load(inertia). is there any formula or calculation then please give me. i shell be very thankful to all of you. Thank,s and Rgard,s.
what is the ka rating of mccb. and how it is decided .
Hi, My plant daily consumption is calculated as 3.8MWH but my supplier has sanctioned an power of 2.6MW per day. how can i equal or distinguish this two factors
Please specify the parts of VCB&ACB
i want to know that what is the eligibility critaria for ongc exam?