Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


If the supply voltage is same (say 440V) whether a system
designed for 60 Hz frequency will work with 50 Hz frequency
or not , if so pl. give clarification.

Answers were Sorted based on User's Feedback



If the supply voltage is same (say 440V) whether a system designed for 60 Hz frequency will work w..

Answer / joysbag@gmail.com

E=4.44(freq.)x(fluux density).

if E is constant - freq is inversly proportional to Flus
density.

Hence with 10% decrease in freq the flux density will
increase by 10% which may bring the transformer at
saturation. Hence it may work but not advisable.

Is This Answer Correct ?    11 Yes 1 No

If the supply voltage is same (say 440V) whether a system designed for 60 Hz frequency will work w..

Answer / shahin

Dear all I've seen that all r telling dc motor, ac motor,
converter etc. ABB has asked for a system not for motor/
inverter. As the equaiton of joysbag reduction of frequency
of 10% will cause increment of 16.67% of flux. Though the
system is designed about 60Hz. Then the system component
may be malfunctioning. All of equipments of the system must
be changed as frequency has changed.....

Is This Answer Correct ?    10 Yes 1 No

If the supply voltage is same (say 440V) whether a system designed for 60 Hz frequency will work w..

Answer / upendra

the life of the equipment will be reduced

Is This Answer Correct ?    8 Yes 3 No

If the supply voltage is same (say 440V) whether a system designed for 60 Hz frequency will work w..

Answer / harsh

joysbag has given the perfect explanation

Is This Answer Correct ?    4 Yes 0 No

If the supply voltage is same (say 440V) whether a system designed for 60 Hz frequency will work w..

Answer / sanjeev kumar

yes system will work with unproper way but the system are
designed as per basic parametre like frequency, voltage,
current,. if we changed the parametre system work with
abnormal way.

Is This Answer Correct ?    2 Yes 0 No

If the supply voltage is same (say 440V) whether a system designed for 60 Hz frequency will work w..

Answer / maheswaran

iron losses such as hysteresis and eddy current losses are
proportional to the frequency of the supply.. so the
frequency increases,obviously losses will increase

Is This Answer Correct ?    3 Yes 2 No

If the supply voltage is same (say 440V) whether a system designed for 60 Hz frequency will work w..

Answer / rameshpaulaian

Its work both 50Hz and 60Hz , but the output is diff from
each.
Ex: Fan, Speed of fan at 60Hz< Speed of Fan at 50Hz.

Is This Answer Correct ?    5 Yes 4 No

If the supply voltage is same (say 440V) whether a system designed for 60 Hz frequency will work w..

Answer / glen saldanha

definately the electronic appliance such a tv will not work
as the calculation of capacitor and inductor rating is
based on 50hz changing the frequnecy to 60 hz will change
the valve and the electronic appliance will behave abnormal

Is This Answer Correct ?    2 Yes 2 No

If the supply voltage is same (say 440V) whether a system designed for 60 Hz frequency will work w..

Answer / naveen

it depends on the application, each eqipment is allowed for
some variation in the parametr. For Ex in case of induction
motor upto 5% variation is allowed in the frequency.So the
behavior of system depends on how much sensitive to that
parameter.

Is This Answer Correct ?    0 Yes 0 No

If the supply voltage is same (say 440V) whether a system designed for 60 Hz frequency will work w..

Answer / tarun aggarwal ymca

actually certain equipment work on the frequency of power
supply such as oscillators or frequency changer used to
trigger the ckt . since frequency has been changed the
resulatnt triggering angle get chandged which offer un
predictable result .
while if a d.c motor is given 50 Hz it commutation process
is designed in such a way that is frequency increase it will
led to short circuiting

Is This Answer Correct ?    1 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

What is the difference between earth fault protection of motor feeder with CBCT and Without CBCT ?

0 Answers   Enmas, Michelin, Reliance,


Define unilateral circuit?

0 Answers  


1)we r having one problem .one dry type transformer(6.6KV/433V)is taking high magnetizing current on delta connected HV side of "U" phase when compared to other two phases.could any body tell the reason why it is happening? 2)why CT secondary side protection core has got higher winding resistance when compared to that of metering core of same CT?

2 Answers  


A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is onbserved the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?

1 Answers  


how does the terminal voltage of transmission lines increase when a capacitor is connected???? This happens not only in transmission lines but also in all circuits. How??? When a capacitor is connected in a transmission line, capacitor also takes energy from the same supply. But how is it able to increase the terminal voltage??? Practically What sequence of events happen during increase in voltage???

0 Answers  


actual rated capacity of a disc insulator??

5 Answers   OPTCL,


what is ideal insulator. what are its parameter. Is poecelain insulator comes under this category.

3 Answers  


definition of transformer

10 Answers  


wat is the advantage of increse in frequency?how the powersupply range decreses as the frequency increses?like in america,it uses 110 ac and 60 hz?

4 Answers  


Merits & Demarits of Oil circuit & Air circuit breakers ?

0 Answers   Genco,


What you have to see in transformer after week, month?

0 Answers  


If we tell 60 sq.mm. 3-1/2 core cable,then what does it mean ? 1) Each core section in the whole cable is of 60 sq. mm. 2) The whole cable is of 60 sq. mm. which is sub-divided into 3-1/2 core.

3 Answers   Cura HealthCare,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)