My requirement is 1VA,50/5A Current Transformer for
Metering .If I select 15VA , 50/5A CT.Is there any
possibility of Technical Problem ?
Answers were Sorted based on User's Feedback
Answer / c r venkatesh
Absolutely no problem.you can always use higher burden CT'
without any problem
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / roy
Hi ,
Yes there is . and a highr rated VA is never recommented
for metering ( again it depends the accuracy but still not
used as per IEC)
Note:The accuracy class will not be guaranteed for burdens
above rated burden or below 25% of the rated burden.Check
IEC 60044
Amd more interstingly , we are allowing or excepting to
saturate this metering core during fault to protect the
metering Equipment reff. IEC 44
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / chandru_williams
no problem at all when we increase the burden . But It
should be noted that the current ratio should not be
increased, since it leades to sensing problem which inturn
hinders the metering values.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / anbuselvan
No problem.
Bcaz CT is an Instrumental Transformer(i,e.,Measurement of
High rating current) to measure only Current.
So there will be no of tapping for each range of current.So
that it will easily sense the rating which u set.
Here both your current rating is same.so no problem at all,
even if the voltage varies.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / satvinder kumar
50/5 1va is suitable for bar primary ct if you go for
higher 15 va then it is good to opt wound primary ct{WPL}
OTHERWISE THE SIZE OF THE CT WILL INCREASE
| Is This Answer Correct ? | 1 Yes | 1 No |
What will be in Mahagenco Trade Test Exam? I want to know the same.
In what situations relays are used in Circuit breaker? In Above what rating of Circuit breaker the relays are used? Why relays are not used for CB like MCB?
what is meant by oil filled power & distrubution transformer ? if anybody know the link of detail about above transformers means plz send it i have interview on this week ? plz help me
How do you reset circuit breaker?
1 Answers Bhel, Kaveri Steels,
Briefly describe your ideal job?
What is pole of the system?
transformers parts & function of each parts
25 Answers Amara Raja, Bhutan Ferro Alloys Limited, Breather, Electrical, Electrical Tech, ERDA, GVK, Juniper Networks, Matrix, Mechanical, NFL, Oracle, Pyramid Plastics, RPPL, RRB, Siemens, TCS, Tulip Silk Mills,
Electricity sometimes can be dangers , sometime got shoked form it . It is because of volatge or Current
how synchronous generator can be used as synchronous condenser?
Y phase's (RYB) r only 3,not 4 or 5?plz answered in breif?
1 Sq.mm ( Aluminium Cable ) = How much Amphere ( AMP )
How to select the earthing transformer,for DELTA TO DELTA TRANSFORMER OR ALTERNATOR SIDE.Pls post your answers and calculation.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)