A three phase load, around 4 km away from the 11/0.433KV
distribution transformer (Neutral of Transformer is
solidily earthed) and consisting of mainly very costly and
sensitive electronic equipments is giving trouble due to
high voltage difference between neutral and body earth.
Whether this problem can addressed by connecting neutral at
the load point solidly to earth?
Answers were Sorted based on User's Feedback
Answer / parul
Check the load circuit properly.Check the transformer at
open and short circuits.Isolate the neutral earthing in the
substation transformer and check the voltage in all phases
to find out whether transformer is the problem or your load.
After considering all above checks you may do the earthing
of neutral point in your load.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / velusamy
check the overall earth pit resistance value and it
should be less than one ohms
| Is This Answer Correct ? | 1 Yes | 1 No |
It is an absurdity to try to provide 433 volt electrical
service to a load that is 4 KM away. You need to install 11
kv line to the load and then install the transformer. You
won't have a problem. There is always a difference between
the earth and a neutral. If that is a problem, bond them
together. They should be anyway.
| Is This Answer Correct ? | 0 Yes | 0 No |
Why LT cables are not sized based on short circuit capacity.
CAN ANYBODY EXPLAIN WHAT ACTUALLY MEAN BY THE PHASE DEFFRENCE? R,L,C CIRCUITS?
what happened if power factor is "1"
Amoung all classes of electric machines, why the transformer uses oil as one medium of cooling?
what is a kit kat fuse?
why surge suppressor in vaccum circuit breaker and it is only in motor feeder why not in tranformer feeder?no surge suppresor in ocb in motor feeder?
what are the types of cooling systems used in motors?
Why soda is added with water in Lrs of Sliipring motor…to Increase or decrease resistance of water?
Please provided formula for calculate the cable size from step up transformer to M.V panel, run overhead aluminum cables, total load is 5mega watt, total length 900 feet.
How many points can we have in AC Circuit? Show by giving suitable example?
What is a signal flow graph?
if a 3phase motor runnig in star delta starter with full load of its,and its rated 15 amps.now we conneted over load thermal relay at its main contactor,here what will be our amps sittings?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)