Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


A three phase load, around 4 km away from the 11/0.433KV
distribution transformer (Neutral of Transformer is
solidily earthed) and consisting of mainly very costly and
sensitive electronic equipments is giving trouble due to
high voltage difference between neutral and body earth.
Whether this problem can addressed by connecting neutral at
the load point solidly to earth?

Answers were Sorted based on User's Feedback



A three phase load, around 4 km away from the 11/0.433KV distribution transformer (Neutral of T..

Answer / parul

Check the load circuit properly.Check the transformer at
open and short circuits.Isolate the neutral earthing in the
substation transformer and check the voltage in all phases
to find out whether transformer is the problem or your load.

After considering all above checks you may do the earthing
of neutral point in your load.

Is This Answer Correct ?    1 Yes 1 No

A three phase load, around 4 km away from the 11/0.433KV distribution transformer (Neutral of T..

Answer / velusamy

check the overall earth pit resistance value and it
should be less than one ohms

Is This Answer Correct ?    1 Yes 1 No

A three phase load, around 4 km away from the 11/0.433KV distribution transformer (Neutral of T..

Answer / wareagle

It is an absurdity to try to provide 433 volt electrical
service to a load that is 4 KM away. You need to install 11
kv line to the load and then install the transformer. You
won't have a problem. There is always a difference between
the earth and a neutral. If that is a problem, bond them
together. They should be anyway.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Why LT cables are not sized based on short circuit capacity.

3 Answers  


CAN ANYBODY EXPLAIN WHAT ACTUALLY MEAN BY THE PHASE DEFFRENCE? R,L,C CIRCUITS?

5 Answers  


what happened if power factor is "1"

9 Answers   Reliance,


Amoung all classes of electric machines, why the transformer uses oil as one medium of cooling?

4 Answers  


what is a kit kat fuse?

5 Answers   TCS,


why surge suppressor in vaccum circuit breaker and it is only in motor feeder why not in tranformer feeder?no surge suppresor in ocb in motor feeder?

1 Answers   IOCL,


what are the types of cooling systems used in motors?

2 Answers  


Why soda is added with water in Lrs of Sliipring motor…to Increase or decrease resistance of water?

1 Answers  


Please provided formula for calculate the cable size from step up transformer to M.V panel, run overhead aluminum cables, total load is 5mega watt, total length 900 feet.

0 Answers   SK Engineering,


How many points can we have in AC Circuit? Show by giving suitable example?

3 Answers  


What is a signal flow graph?

0 Answers  


if a 3phase motor runnig in star delta starter with full load of its,and its rated 15 amps.now we conneted over load thermal relay at its main contactor,here what will be our amps sittings?

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)