A three phase load, around 4 km away from the 11/0.433KV
distribution transformer (Neutral of Transformer is
solidily earthed) and consisting of mainly very costly and
sensitive electronic equipments is giving trouble due to
high voltage difference between neutral and body earth.
Whether this problem can addressed by connecting neutral at
the load point solidly to earth?
Answers were Sorted based on User's Feedback
Answer / parul
Check the load circuit properly.Check the transformer at
open and short circuits.Isolate the neutral earthing in the
substation transformer and check the voltage in all phases
to find out whether transformer is the problem or your load.
After considering all above checks you may do the earthing
of neutral point in your load.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / velusamy
check the overall earth pit resistance value and it
should be less than one ohms
Is This Answer Correct ? | 1 Yes | 1 No |
It is an absurdity to try to provide 433 volt electrical
service to a load that is 4 KM away. You need to install 11
kv line to the load and then install the transformer. You
won't have a problem. There is always a difference between
the earth and a neutral. If that is a problem, bond them
together. They should be anyway.
Is This Answer Correct ? | 0 Yes | 0 No |
Is it required to lay GI wires along with GI/MS conduits from one point to another point though separate earthing cable is conncted from DB to Socket?
Why colled 440V to 3-phase supply.
Is 3 phase induction motor can work as a generator?? if so why & how??
For 7.5kw star delta starter how to calculate 1. Mccb rating 2. Contactor rating 3. Over load relay rating
What is the difference between single core 2 wire and single core 3 wire system? Which application we are using this? and for What purpose we are using this?
Why current shoots up in the secondary on the knee point voltage during saturation test of CT? How core saturation effects the secondary current (while the primary side is open)? What the logic behind this?
can u give me a brief idea about power line carrier communication ??
60 watts bulb and resistor home heater is connected in series and 230v is given to the circuit. The heater is giving some amount of heat. If instant of 60 watts bulb replace 100 watts bulb what will be the output of the heater?
What does a Bode plot tell you?
how MW increase when steam input increase in turbine.
1. The DC generaror,s induced output emf is connected with a DC motor(as load). when increasing the load of the motor by using brake drum or any way. what are the parameters will changes in both motor and generator(voltage, current, resistance, frequency, speed, torque, power, flux etc...) 2. Similarly for AC generator and AC motor 3. similarly if using DC batteries instead of DC generator, What happens?
What is thermal relay and how it is works in transformer please explain