how many amps in 1 KVA? V=440v, PF=0.8 and FREQ=50Hz
Answers were Sorted based on User's Feedback
Answer / raeworx
SINGLE PHASE CIRCUIT three phase circuit
V(PHASE)= V(LINE)/1.732 KVA = I*V*PF*1.732
= 254V I = KVA/V*PF*1.732
THEREFORE I = KVA/V = 1000/(440*.8*1.732)
= 1000/254 = 1000/ 609.7
= 3.94A = 1.64A
Is This Answer Correct ? | 10 Yes | 9 No |
Answer / sushant
KVA = (1.73*VICOS PHI)/1000
1 = (1.73*440*I*0.8) / 1000
I=1000/(1.73*440*0.8)
= 1000/608.96
I = 1.64 A
There is no ralation between volt,ampere & freq
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / deepak
KVA(Apperent Power)=1.732 * Line voltage * line Current(It
is in Three Phase System)
According to above formula
I= KVA/1.732*Line Voltage
I=1000/1.732*440
I=1.312Amp.
Is This Answer Correct ? 7 Yes 4 No
0
Ameerlal
Re: how many amps in 1 KVA? V=440v, PF=0.8 and FREQ=50Hz
Answer
# 13
kva=1.732*v*i*cos
i=kva/1.732x440x0.8
i=1.6A
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / deepak g shinde.
When Kva known I = Kva*1000/V*1.732
I=kva*1000/1.732*440
I=1*1000/1.732*440
I=1.31 Amps
I consider this only for three phase & not for single
phase ,because there is very rare chance of 440v in single
phase.
Is This Answer Correct ? | 2 Yes | 4 No |
Answer / pearl ganesh
kva=1.732*v*I*p.f
I=kva*1000/1.732*440*0.8
I=1*1000/1.732*440*0.8
I=1.640 Amps
Is This Answer Correct ? | 16 Yes | 19 No |
Answer / suresh m s
kva=1.732*v*i*cos
i=kva/1.732x440x0.8
i=1.6A
Is This Answer Correct ? | 3 Yes | 6 No |
Answer / pradeep baliyan
I KW = V * A * 1.732 * .8 / 1000
(For 3 Phase)
Kva = V*A*1.732/1000 (3 phase, V= 415)
Kva =V*A/1000 (1 Phase, V= 220)
Is This Answer Correct ? | 4 Yes | 12 No |
What happened when the field winding of dc series motor is open?
what is B , c & d curves in MCB characteristics i e Full Form of B , C & D . sir please give me answer
when we catch any one of the phases with our both hands in air(without touching ground),our body acts as a conductor.is it correct.please clarrify it.
Can we use MCCB with Auxiliary Contact in place of Contactor in a AMF System.
How to decide the input and output circuit breaker for a 1600kva transformer.Is there any calculation is involved.
xpression 'document.FrmQF.myemail' [
Dear all, Can anybody tell me that how to choose CT for a specific load? I have a 200kw induction motor, which ratio CT should be installed? Is there a formula or calculation that determines the CT ratio for a load? Regards.
what is the difference between earthed and unearthed cable?
24 Answers Cords Cable, Essar, Torrent Power,
What is a dominant pole?
What is correction factor in Tan delta test?
what will happen if dc machine are supplied by ac source??
what is diff between Ground/Earth & Neutral?