Answer / ritesh
actually setting of over load relay depends on the duty of
motor.if duty of motor is 2 then set relay at full load
current.if it is 2.1 then set relay at 10% higher then full
load current so on...........
Is This Answer Correct ? | 9 Yes | 3 No |
125% of the motor full load current require for Overload relay.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / bijay
RELAY SETTING REQUIRES TWO THINGS CURRENT AND TIME
CURRENT SETTING CAN BE UP TO 20 TO 30 % FOR SMALL MOTORS
AND UPTO 10% IN MV MOTORS.
BUT DONT FORGET FOR MUCH TIME U R OVERLOADINIG THE MOTOR.
TIME SETTING IS ALSO IMPORTANT...
THIS DETERIORATES ITS INSULATION
Is This Answer Correct ? | 11 Yes | 9 No |
Answer / exxon
Is it safer to find out the spec about the motor winding
before deciding the overload relay settings. Every motor
manufacture has detailed spec. about is motor winding such
as insulation class:. Overloading the motor full load
current will deteriorates the insulation and winding life.
Is This Answer Correct ? | 8 Yes | 6 No |
Answer / suresh
set the overload setting standerd draw currents 10% extra
but less than rated current
Is This Answer Correct ? | 6 Yes | 9 No |
How can we deside Short Ckt level of electrical System,Breakers etc.please provide formula to find SC of HV side & LV side
when power transformer is flashed which gas is produce in side?
For a 500 MVA 400/220/33KV transformer following data given HV power = 500 MVA IV power = 500 MVA LV power = 5 MVA If input power is 500 MVA then how output power is (500+5)MVA. Can anyone help
slor cell made?
If we need4× 50mm sq cable but it's not available so we can pull 4×25mm sq 2cables
what are the 6 terminals of the motor plss give me in details
in a three pin socket y the pin of earthng is longer n bigger...?
A Question Like A Wire Is Wound Whose Resistance Is Some 132. 44647 Ohms. If A Voltage Of 30 mv, 296 Ma Current Is Applied To It What Is The Resistance.
what are the analog quality input for protection function?what are minimum reqiments?
Name of the relay of low lub oil presuure in DG sets
How to check VFD outgoing voltage
i have a motor 55kw how u will calculate cable specification for this motor