how to calculate induction motor rating (HP) if name plate
is missing from motor at site condition ?
Answers were Sorted based on User's Feedback
Answer / senthil kumar.i
while name plate is missing,
first we are taken the details from the motor bellow
1. torque
2. Motor Rpm.
sutitute the given formula.
BHP = 2*3.14*T.N / 60 * 746
where T is torque and N is motor Rpm.
torque unit is nm.
we can get the Missed name plate motor HP.
| Is This Answer Correct ? | 46 Yes | 28 No |
Answer / manoj
1. Switch on the motor & measure the current (i) using Clamp
meter.
2. The calculated current (i) should be multiplied with
250Watts.
3. The result value should be divided by 230Volts i.e the
present voltage ratings.
4. The result of the step 3 will be the induced motor
ratings in HP.
This is illustrated with a small example below:
Assume that a motor of 5HP 3-phase is not having a name plate.
For 5HP motor, the current ratings will be around 7amps.
As we all know that, 1amps=250Watts.
So, multiply 7amps with 250Watts i.e 7x250=1750
The result answer 1750is divided by present input voltage
i.e 230V.
1750/230=7.6
Hence the result answer is the induction motor's rating in HP.
Another easy method to calculate this is:
check the current & divide it with 1.39(current rating of 1
HP motor)
the result answer will be the motor rating in HP
| Is This Answer Correct ? | 26 Yes | 16 No |
Answer / seshasai bagadi
APPLY 440 VOLTS AT NO LOAD TO THAT MOTOR AND FIND THAT NO
LOAD CURRENT BY CLAMP METER.,
AS INDUCTION MOTOR TAKES 30 % OF FULL LOAD CURRENT AT
NOLOAD .,HENCE RATING CAN FIND BY USING..
P=(1.732)(V)(I)
WHERE V-RATED VOLTAGE(440V)
I-FULL LOAD CURRENT (CALCULATED)
P-RATING OF MOTOR IN KW
ASSUME UNITY POWER FACTOR
| Is This Answer Correct ? | 20 Yes | 12 No |
Answer / sajid khan
check the current by clamp meter on no load condition.
multiply this no load current to 2.5-3, and hence you will find your final answer.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / ramendra shukla
As we know the Relationship of Mech. HP with Elect. KW is-
HP = 0.734 KW
P= VI in KW (let PF is unity or pure resitive load)
First we will get the the Voltage V, and then the current,
C in amps By this we will calculate the Horse power ,HP.
Lets have an example
Q:- A motor is taking the current as 30 amps & the voltage
is having 420 calculate how much HP it have??
ANS :
We know HP =0.734 KW
& P= VI cos@ (let cos @=1 or pure resitive load)
then
P = 30x420x1 KW
= 126 KW
So,
HP =0.734x126 :=92 HP
| Is This Answer Correct ? | 29 Yes | 44 No |
Can the same motor be operated in both direction ?
In an electrical power supply,why if neutral phase of a 3phase supply fail over current occur but if it's single phase supply neutral phase fail low current occur?
What is the difference between Isolator annd Circuit Breaker.
21 Answers ABB, Lanco, NTPC, Power Grid, RInfra,
what is the difference between UPS & Inverter
What is the function of a capacitor in a ceiling fan?
Why slip ring ind. motor power consumption is low compare to induction motor .same 90 kw motor used same load output
Why Transformer in KVA?
41 Answers APCPDCL, Apollo Power, College School Exams Tests, Electrical Tech, Hitech, HP, L&T, MDL, Oil and Gas Jobs, TATA,
What is WLD System????
3 Answers Emerson, HCL, Honeywell, Tata Communications,
will 1050kva DG set withstand for back charge of 16MVA transformer
what deffrence between KW $ KVA ?
how to check the stabilty test for generator differential protection
The slip during plugging operation is given by= A 1-s B 2+s C 1+s D 2-s
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)