Why Lightning arrester used? Can we use piece of iron as a
core material of transformer, if No, why? In CRGOSS
material what is meaning of cold rolled grain oriented? Why
Impegrenation of Transformer is done? Properties of
Insulator? what is phase angle? Testing of transformers
(Routine & Monthly)?
Answers were Sorted based on User's Feedback
Answer / rahul thakur
Lightning arrester is used to provide path to unwanted excessive currents due to lightning strokes,to the earth which is nearly equivalent to zero potential.
Iron may be used but it will lead to high reluctance path and hence a greater losses like hysteresis loss and eddy current loss.
Cold rolled grain oriented means that if the path of flow of magnetic field is along the rolling direction,minimum reluctance is offered.
phase angle is the angle by which the emf induced in the secondary side lags the current.
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / badshah
Lightning Arrestor is to bypass the lightning to earth by
which we can protect the equipments from high voltage of
lightning
Piece of iron can be used as a core but it will cause more
eddy current to flow through the core & more iron
losses..that's why the cores are laminated
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / dhiraj
In power system when lightning occures it brings ehv to the
earth which can damge your Power system badly to avoid that
we must use arresters with solidly ground to divert the
lightning path,
If we use Iron as core material the core losses will be
like hell which will make trafos efficiency to very less
and due to that eddy current increase will make heating of
trafo.
for further details read power system engg book.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / deepak
lightning arrestor is a highly pointed device , which can
make the ehv coming from the lightning to split into
positive and negative ions...this ions are absorbed by the
carriers and they are byepassed to the earth ,which is
basically a zero potential.we cannot use iron because eddy
current produced in the iron will be very high .
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / veer
it is used only for protecting our equipment from the
thunder light. All current bypass through this.
if we use the coil/core then there will be high reluctance
and due to have an rolling iron there will be eddy current
and hysterisis loss
| Is This Answer Correct ? | 0 Yes | 0 No |
We have 250 KVAR cacitor bank & our average load is 200kva but our power factor is average 0.66 how can we maintane it? how can we balance our load?
why Induction Generators are not "Black start" ? and apart from WTGs where this types of generator are generally used?
why tertiary winding is used in transformer with diagram?
How do performance buccholz relay testing in power transformer
Why are calling leading power factor is a capacitive load?
why return path in terms of neutral is required please give a relevant answer
what is the diffrence between single phase and three phase
State superposition theorem?
1.why should we connect the measuring instruments in l.v side in short circuit test of a transformer? 2.why the power factor is less in open circuit test of a transformer?
wht is the purpose of the earth electrode other then earthing
What is the meaning of 'A synchronous motor floating on line'?
what is the differance between MC61C and MC61A relay of L &T make.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)