1.generator rated as 1000 mva,11kv .8 pf what will 0.8 pf
will indicate?
1.max pf it can supply 2.min pf it can supply
like this 4 options there what is answer.explain
Answers were Sorted based on User's Feedback
the above mentioned genrator Ans is 1.
it can supply max. load i.e 0.8 pf means 80 percent of rated
1000*0.8=8MW.
| Is This Answer Correct ? | 11 Yes | 2 No |
i agree with Mr Reddy.
Generator rated at 1000MVA at 0.8 pf 11Kv
In terms of KW the prime mover had been designed for this Gen is 1000 MVA X 0.8 = 800kw, any thing more can destroy your prime mover in the long run
now the alternator part is 1000 MVA AT 11KV
The max amps it can carry is 1000000/1.732/11000= 52.5A /phase
now you can operate the generator at any pf you want as long as you do not exceed 52.5 amps per phase.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / sreenivasalareddy
I will deliver (generator design)800mw power wether it
running at .8 PF or unity pf
When Generator runnig at upf we should alert we should not
load alternator to its rated current
Because your out put power will become 120 % almost ,Which
is not design for this load (Primover)
As for as my concerned pf is restrited to protect promover
and alternater eigher way
| Is This Answer Correct ? | 5 Yes | 2 No |
about your self?
4 Answers Hyundai, US Technology,
Genreally distribution transformers are having Star/delta connections to provide phase and neutral to the consumers. Is the neutral of the star conncted secondary grounded in these transformers?
which metal use as a electrical shunt?
where can the transformer having vector group Yny0 be used??
0 Answers GK Power, NEA, Petrotech,
WTA used cb?
What is diversity factor in electric installations?
if a 3phase motor runnig in star delta starter with full load of its,and its rated 15 amps.now we conneted over load thermal relay at its main contactor,here what will be our amps sittings?
The specific heats of the gas at constant pressure and constant volume are respectively 1.0 kJ/kg K and 0.72 kJ/kg K; the value of R for the gas is
upto how much low RPM we will run the commercial motor which is run through VFD without any problem occurs in motor.Motor rating Duty is S1 & RPM is 1400.
trasformer ratting
if any one phase of the 11kv/415v distribution transformer not delivering the supply voltage what will happen
ouestion for the post of section engineer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)