1.generator rated as 1000 mva,11kv .8 pf what will 0.8 pf
will indicate?
1.max pf it can supply 2.min pf it can supply
like this 4 options there what is answer.explain
Answers were Sorted based on User's Feedback
the above mentioned genrator Ans is 1.
it can supply max. load i.e 0.8 pf means 80 percent of rated
1000*0.8=8MW.
Is This Answer Correct ? | 11 Yes | 2 No |
i agree with Mr Reddy.
Generator rated at 1000MVA at 0.8 pf 11Kv
In terms of KW the prime mover had been designed for this Gen is 1000 MVA X 0.8 = 800kw, any thing more can destroy your prime mover in the long run
now the alternator part is 1000 MVA AT 11KV
The max amps it can carry is 1000000/1.732/11000= 52.5A /phase
now you can operate the generator at any pf you want as long as you do not exceed 52.5 amps per phase.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / sreenivasalareddy
I will deliver (generator design)800mw power wether it
running at .8 PF or unity pf
When Generator runnig at upf we should alert we should not
load alternator to its rated current
Because your out put power will become 120 % almost ,Which
is not design for this load (Primover)
As for as my concerned pf is restrited to protect promover
and alternater eigher way
Is This Answer Correct ? | 5 Yes | 2 No |
Why don't we provide SURGE ARRESTORS for Transformer feeders?
what is reactive and active power?why we need power factor correction?
what is the Transformer Impedence?How can calculate?
Can we use the ceiling fan regulator to run drill machine having 2000 watt power consumption?
Hi,Any one has idea regarding the KPTCL Recuirtments for AE'e & JE's for the year of 2009-10???Kindly help in regards..
which motors are used in electric traction?
what is the pulse and audio frequency transformer? what is different between induction regulators and tap changing transformer?
what is formula of illumation calculation
in 6.6 kv vaccum circuit breaker vaccum bottole vaccum capacity ????
how to calculate the lightning arrester conductor @ no of earth pits required
What are various impedence in any machine
2 Answers Engineers India Limited, NTPC,
what is the minimum distance between substation wall and LT panel outer surface?