i want to Measure the Difference pressure of Packed distillation Column of height 3 mtr. h.p. side connected to
bottom & L.P. side connected to the top , so tell me what
will be THE URV & LRV of that D.P. transmitter?
Answers were Sorted based on User's Feedback
Answer / vishal khalasi
o to 76.2 mmH2o that is the correct range...
Is This Answer Correct ? | 0 Yes | 0 No |
If you want to mesure a differential pressure of Packed
distillation Column and currect out put signal then
instrument mesuring rang should be higher than required
measuring renge.
URV >3000 mmm WC ( Say 4000 mm WC)
LRV= 0 mm WC
calibrate it 0 mm WC to 4000 mm WC .
Is This Answer Correct ? | 0 Yes | 3 No |
why pressure 3-15psi is used as industrial standard and what is the reason
2 Answers JAL International, UltraTech,
what is compensation? temprature & pressure
How can we test a bently nevda 3500/42M accelerometer monitor card by simulating it with test equipment?. what king od of signal (milli volts or volts or or resistance ) we should feed in the terminals of the card?
what is the analog input , analog output , digital output, digital input geven to the MSSV , CBD, IBD , START UP VENT , BOILER FEED PUMP , AOP, CEP , ETC
1 Answers Bharat Biotech, TATA,
What are the different type of instrument used in cement industry with uses
WHAT IS THE CAM POSITION IN CONTROL VALVE POSITIONER ? WHY IT IS USED?
hi! i want to know about mpse exam.
What is standard of DCS panel design?and what is step of DCS panel design?wiring and type of connector(screw or DB connector)
I am using 971 Enraf radar level transmitter for LPG tanks ,the tank side indicator gives the error code 999999999FL can any body give me any diagnostic for this issue?
What is intrinsically safe system?
what is plc? breif explain
how to calibrate transmitter