how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / virendra

Considering Powe factor 0.8
Kw = KVA*.08
KW = 100*0.8
= 80 KW
w = 1.73 * 415 * Il * 0.8
80000 = 1.73 * 415 * I1 * 0.8
I = 80000/ 1.73*415*0.8
= 139 Amp

You can choose the cable which current carring capacity per
phase is on or above 140 Amp

By considering the future expansion of load the 180 Sq.mm
AYFY cable is ideal.

Is This Answer Correct ?    18 Yes 2 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / prashant singh

KVA=uder root3*V*A/1000
A=Under root 3*415*KVA/1000

Is This Answer Correct ?    22 Yes 7 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / abdulsubur

WE CAN GET FROM THIS REALTION
KVA=KW/KVAR
100*85=85KW
THEN FIND CURRNET FROM P=ROOT 3 VICOSPHI FORMULA THEN FIND
CURRENT AND THEN LENTH FROM THE MV=VD*1000/L*I

Is This Answer Correct ?    11 Yes 6 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / brijesh shakya

Before calculating size of cable, phase & voltage should be
clear then after we can calculate the current of load by
this formula
P=root3*V*I
I=P/(root3*V)
Accodingle we can select the size of cale.

Is This Answer Correct ?    8 Yes 3 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / jack

Depends on what voltage you working with.

P = V*I

You got P and V, find what your I is.

Then use a cable selection book from, eg. Olex, choose your
cable from there.

Is This Answer Correct ?    7 Yes 14 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / jiwanjot

i think something is wrong with question ...load can never
be in KVA it should in kw if we talk about motor.....

Is This Answer Correct ?    5 Yes 15 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / mehul g. c.

if your load is single phase then you should use 3.5c x 185
sq.mm alu. Armoured cable.

Is This Answer Correct ?    1 Yes 12 No

Post New Answer

More Electrical Engineering Interview Questions

why 30 ma elcb is used ?why cant 100 ma?

3 Answers  


why CT output is always raetd 5.regardsof primery curre.

3 Answers   ABB, BARC,


How we calculate the current carriying capacity of the different sizes of Aluminium busbar ?

3 Answers   ABB, Raj Process Equipments, Visa Steel,


What are the fire Estingushers use in electrical fire?

3 Answers  


what are the different methods for the starting of a synchronous motor.

0 Answers  






why capacitor offer reactance to alternating current?

1 Answers   Electrical,


In 11kv transmission line whats the maximum power can be drawn?

1 Answers   Concast, Prestige,


i) in which cases should we go for neutral and where should we go for ground? ii) in domestic supply we are getting 230v a.c.and what is the amount of current?

2 Answers  


how to measure dc earth leakage current?

0 Answers  


what is the pre commissioning test to be carried out on LT power panel at site?

1 Answers  


My load is 15 kw,i want to improve power factor from 0.8 to 0.9,how select capacitor

2 Answers   RIB Software, TATA,


what is zinc diffusion?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)