What is ics,icu,icw of load breaker
Answers were Sorted based on User's Feedback
Answer / mike evans
Circuit breakers are designed with withstand short circuit
currents for a short period of time, defined as Icw for a
period of 1 second. This is designed to guarantee
selectivity of breakers and other devices providing short
circuit current protection. The ultimate breaking capacity
of the breaker is the highest symmetrical short circuit
fault current that the breaker is designed to break, and the
breaker manufacture is required to guarantee this level of
performance for one time only. Ics or service breaking
capacity must be guaranteed at least 3 times.
Realistically, the value of Icu is not practical when
considering fault calculations in a distribution system, and
often manufacturers aim for achieving Ics=Icu.
Is This Answer Correct ? | 147 Yes | 26 No |
Answer / ravikumar varatharaj
Icu - ultimate short-circuit breaking capacity
a breaking capacity for which the prescribed conditions according to a specified test sequence do not include the capability of the circuit-breaker to carry its rated current continuously
Ics - service short-circuit breaking capacity
a breaking capacity for which the prescribed conditions according to a specified test sequence include the capability of the circuit-breaker to carry its rated current continuously
Icw - rated short-time withstand current
The rated short-time withstand current of a circuit-breaker is the value of short-time withstand
current assigned
Icm - short-circuit breaking (or making) capacity
a breaking (or making) capacity for which the prescribed conditions include a short circuit
Is This Answer Correct ? | 40 Yes | 9 No |
Answer / tad rybak
To my understanding Icm stands for Short Circuit Making
Capacity.
According to standard IEC 947-2 or BS EN60947, etc.
It is equal to 2.2 x Icu, where Icu means Ultimate breaking
capacity.
Is This Answer Correct ? | 53 Yes | 31 No |
Answer / vyara
Ultimate or rated short-circuit breaking capacity
(Icn - EN 60898)
A breaking capacity for which the prescribed conditions,
according to a specified test sequence do
not include the capability of the MCB (Miniature Circuit
Breakers) to carry 0.96 times its rated current for the
conventional time.
Ultimate short-circuit breaking capacity
(Icu - EN 60947-2)
A breaking capacity for which the prescribed conditions,
according to a specified test sequence do
not include the capability of the MCB to carry its
rated current for the conventional time.
Service short-circuit breaking capacity
(Ics - EN 60898)
A breaking capacity for which the prescribed
conditions according to a specified test sequence
include the capability of the MCB to carry 0.96
times its rated current for the conventional time.
Service short-circuit breaking capacity
(Ics - EN 60947-2)
A breaking capacity for which the prescribed
conditions according to a specified test sequence
include the capability of the MCB to carry its rated
current for the conventional time.
Is This Answer Correct ? | 19 Yes | 20 No |
What are the basic properties of signal flow graph?
is all the servo motors having brake?please specify which servo motors having brake for stop on position and which are not.
if ELCB and RCCB connected in series,what wiil be the result
how to failure indution motor insulation & how to improve heat in motor insulation
0 Answers BHL, EPIL, IFFCO, Micromax,
How to decide the rating of CBCT? We have 6.6Kv switchgear & having 50/1 cbct ,i want to know how this 50/1 A came? On what basis we decide CBCT reting?
at meter room 50 hrc switch installed,but there are not get earthing proper,so what happen?and 11kv transformer out put going in to hrc main 400a three nog each? so earthing is require for all switch? (some customer made earthing at there home.)
0 Answers Ebrahim Textile, Siemens,
what is the formula or method to calculate RESIDENTIAL,COMMERCIAL & INDUSTRIAL load power?????
how the specific fuel consumption of 320 kva deisel genarator set (explain with formulas please)?
in india are trains run by DC or AC? if DC , from where it receives negative potential? because pentograph receives singe potential only?
How many points does a Circuit can have?
HOW TO TEST THE SODIUM VAPOR AND MERCURY VAPOR LAMP ?
Percentage losses in power generation?