hi vishok this is noor plz tell me what type problems will
occured i use T/C in the place of RTD in (FEED WATER
TANK),plz send ur e-mail address to my ID
(mail2noor.hyd@gmail.com)
Answers were Sorted based on User's Feedback
Answer / bm
No problem will occur if you use T/C inplace of RTD.
However as the temperature in feed water tank is less, and
RTD has better linearity,accuracy in lower temperature,
RTD's are preferred over T/C.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / solomon
No problem.costwise T/c better.accuracywise RTD better.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / g.ramki
hi noore use RTD for good in low temp application,feed wtr
tk temp max 100deg.rtd will give good accuracy if u want to
change u ave to lay tc cable.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / arun
We use RTD in place of T/c because rtd have the greater
accracy in comparation of T/c.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / goutam
Fine Noor ,you wont face any problem but in case of accuracy rtd is better than t/c and to that you need to do the connection as for an rtd.
| Is This Answer Correct ? | 0 Yes | 0 No |
Explain the usage of the PLC system?
Explain the combusion chamber
hello.my friends.i am an electronics & instrumentation engineer.i want to know Q1.why lugs use in instrumentation cable termination? Q2.if limit switch not working what to do?
what are the steps to commissioning a DCS system?
Can a pneumatic control valve work without positioner?
Why all the drains(Gland sealing,ESV,Casing inlet etc) are directly connected to the flash tank instead of hotwell of the condensor in the power plant? My Email Id:naba02222@gmail.com
Why we are using 4-20 mA as Analog signal transmission other than 3 to 19 or 2 to 18 or 6 to 22 like wise ? What is the reason behind using 4 & 20 mA? Can anyone give proper technical reply ?
Working principle of magnetic flow meter ......and calibration procedure of e+h magnetic flowmeter...
Why the Air Tank Accumulators required for the single acting actuators SDV's or BDV's as I see in some Schematic diagrams of ROTORK ??
when we are using HART COMMUNICATOR why we are using 250 ohm resistance while using HART COMMUNICATOR.
Why is it necessary to use compensation leg to measure the liquid level in a closed or pressurized tank?
what diffrence b/w plc s7200,300,400
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)