hi vishok this is noor plz tell me what type problems will
occured i use T/C in the place of RTD in (FEED WATER
TANK),plz send ur e-mail address to my ID
(mail2noor.hyd@gmail.com)
Answers were Sorted based on User's Feedback
Answer / bm
No problem will occur if you use T/C inplace of RTD.
However as the temperature in feed water tank is less, and
RTD has better linearity,accuracy in lower temperature,
RTD's are preferred over T/C.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / solomon
No problem.costwise T/c better.accuracywise RTD better.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / g.ramki
hi noore use RTD for good in low temp application,feed wtr
tk temp max 100deg.rtd will give good accuracy if u want to
change u ave to lay tc cable.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / arun
We use RTD in place of T/c because rtd have the greater
accracy in comparation of T/c.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / goutam
Fine Noor ,you wont face any problem but in case of accuracy rtd is better than t/c and to that you need to do the connection as for an rtd.
Is This Answer Correct ? | 0 Yes | 0 No |
Which types of quections asked in interview for FORMULATION PLANT (PHARMA)
why we are using analytical instrument in plant ?
how many types of thermocouple cable are? give the name of each type.
few questions on RS 232,1 question on relationship of impedance and turns ratio, many questions on flowmeters
What is intrinsically safe system?
who discoverd ohms law?
What is the difference between floating and fixed voltage?
what is commissioning.
what are the sensor types of vibration&speed?n what is proximity sensor?
what is the function of boiler in plant?
What is the difference between local indicator(flow) and flow indicator?
why any measurement made interms of pressure is more accurate ? to be more precise most of the flow velocity is made interms of pressure and it is accurate. what is the reason behind pressure measurement being accurate ?