What power factor maintain you maintain at u r organisation
Answers were Sorted based on User's Feedback
Well so many answers to this simple question. The real
answer as per my experience is 0.85 to 0.9. The minimum
requirement by the Electricity boards is 0.8 to 0.85 or
they will charge a fine. But for industry 0.85 to 0.9 is
optimum and above this you will have to use large capacity
of Capacitor banks which is not practical. Also if
capacitors are too many than this will give leading PF and
this is not good since this leads to higher voltage and
many times has resulted in motor burning or failures, and
permature failure of electical equipment.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / lakshmi shankar pathak
in the industry usually the load is inductive.so i will try to maintain the power factor in the range of .6 to .85
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / suthan prabhu
for industrial load we have to maintain 0.8 to 0.85 p.f
Is This Answer Correct ? | 1 Yes | 4 No |
Can I use star delta connected induction motor for dual supply voltage?
Should the neutral earthing of 33/11KV D-S transformer, be connected to the earth grid?(Yes/ NO) why?
1 Answers HAL, Vijai Electricals,
how much Amp we can put in 1200kva generator?
We need to current density & short circuit calculation at 65kA for aluminium & copper busbar.
what is phantom load, Give any example
Are you connected Transformer neutral eathing with it's body earthing or earthing met of switch yard.? Yes or No ? why ?
Why can't we parallel the secondary circuits of two voltage transformers?
Assume a condition such that two motors of rating 6.6kv,415v are connected to blower,so tell me which motor draw large current give appropriate reason?
what is different between grounding and earthings?
What are the uses of MCB & ELCB ?
CBCT selection
what is the diference between base speed and rated speed in motor