If we connect the capacitor banks for DG set for maintainig
the power factor, it will effect to alternator
windings??????????
Answers were Sorted based on User's Feedback
Answer / gaurav khanduja
we will not have to connect the capacitor with the D.G.
because D.G. work on the principle of AVR(Automatic voltage
regulator)and AVR work always lagging PF. if we connect the
capacitor then it gives leading P.F.And O/P voltage of D.G.
will be vary so we never connect the Capacitor with the D.G.
Is This Answer Correct ? | 15 Yes | 0 No |
Answer / mushtaq
Capacitors can be connected to DG set But, the Power factor should be always maintained below Unity (i.e lag), if it cross beyond the Unity (i.e lead) Alternator's Automatic voltage Regulator get burnt and simultaneously the windings
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pradeep kumar dhar
You can connect capacitors across load to the extent the
reactive power is compensated.Over compensation is
harmful.As a thumb rule 80% compensation is o.k.But then
the voltage should not be allowed to increase beyond limits.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / indrajeet
We can connect capacitors to compnsate reactive power to a
certain limit because in DG set there will not any value
for shooting of Max. demand.One benifit you will get that
your alternator winding will get more life.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / pradeep dhar
The generator is a source of power.You never connect
capacitor across source.The capacitor should be connected
accros load for power factor compensation so as to meet the
reactive power demand.overcompensation is harmful.
Is This Answer Correct ? | 0 Yes | 1 No |
Whar is the KvA rating of 33Kv substation & actual kv rating of power generaating station.
what is the concept of directional power?
How to calculate meter constant @ HT yard
types of arc quenching methodes
HOW DO I CALCULATE OVER LOAD RELAY & CONTACTOR IN DOL STARTER? & in dol why it is require circuit breaker?
i want bhel placement paper for electrical if anybody having pl send to my id kavitha867@myway.com immediately
how to calculate of which rating transformer should be selected? take any example
What happen if we give resistance to the armatuure of a dc motor?a
What is the name of transformers oil filteration equipment?
Dear sir, In our plant have Station Transformer having capacity,i want to know, why LV side 40 - 40MVA is given? & how we can get 6.3 KV supply from tertiary(i.e. Open delta connection), Vector Group YNyn0 - yn0 +d MVA Rating 80MVA / 40 - 40MVA + 26.7MVA Voltage rating 420 (Tap range +6,to -10)81.25% /11.5KV - 11.5KV +6.3KV
why capacitor takes more current