HOW DO I CALCULATE OVER LOAD RELAY & CONTACTOR IN DOL
STARTER?
& in dol why it is require circuit breaker?
Answers were Sorted based on User's Feedback
Answer / x man
for OLR---It has to be Motor full oad current
for Contactor--it has to be 1.5 timmes the motor rated
current.
Circui breaker is used to protect the circuit.
for A tYPR 2 cordination these three componenrs are needed
in the circuits
| Is This Answer Correct ? | 13 Yes | 6 No |
Answer / ermias solomon
in OLrelay 115%*motor name plate current
for contactor use
NEMA table by ermias solomon
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / christopher pino
Refer to NFPA 70 - NEC 2005 (Article: Motor Protection) for
sizing and other consideration.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / barkha
In case of DOL Starter overload relay range depend on full
load current(flc) of the motor it is 2-3 times of flc &
also keep in mind the fuse rating of the motor
| Is This Answer Correct ? | 11 Yes | 15 No |
Answer / nikhil chugh
THE CONTACTOR RATING SHOULD BE 3.5 TIMES GREATER THEN THE
MOTOR CURRENT RATING FOR SMOOTH RUNNING OF THE MOTOR WITH
PANEL
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / k.suresh
motor full load ampes & 6 time higher select OLR AND
Contactor.
| Is This Answer Correct ? | 11 Yes | 27 No |
I have recently seen a transformer which had two primary terminals and was connected between two lines,i would like to know what kind of transformer is it?short discription about it,any advantages,purpose of usage of the same.............
what isthe emf eqation of a transformer
What happen in ups if phase reverse?
how many types erthig
What is the basis for framing the rules of block diagram reduction technique?
the problem faced on star or delta winding connection??
In which of the following case, the rotating magnetic field is reversed? A regenerative breaking B plugging C dynamic breaking D forward motoring
In all analog voltmeters or ammeter showing some small size symbols. as well as a star and in star 2no. digit, resister symbol,and other. what is that's meaning ?
Readings of ER300P Trivector meter
What is different between MCB & MCC & isolator switch
what is difference between megger & Contact resistance meter & its Application?
what is the use of excitation transformer in LAVT PANEL?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)