how you can select circuit breaker for 2000kva transformer?
Answers were Sorted based on User's Feedback
Answer / gaurang
As per Equation
P=route 3 * V *I* cos phi
I=KVA/ rout 3 * V
So for 2000 KVA Transformer and considering Volatge 415 V.
I=2000/1.732 * 0.415
I=2782 A
Considering the breaker rated capacity selection above 2782
A as per Mfg. std.
Circuit breaker capacity will be of 3200 A.
Is This Answer Correct ? | 26 Yes | 0 No |
Answer / ashish patil
First find the full load current of transformer.2MVA
transformer current value comes near 2915 A. consider
overloading capacity 10%. it comes near 3100.
so u can select indor Air circit braker or 4000A
capacity.
Is This Answer Correct ? | 29 Yes | 12 No |
Answer / solver
gaurang you are right
also mukund is right
Dear ashish & sareer,
always remember that the LT side breaker of transformer
is only selected based on rated capacity of LT winding.
i.e. 2782 A in this case.
& no overloading is considered beyond capacity of
transformer winding.
besides that transformer is loaded to 80% of its capacity.
This makes the load current even lesser than the rated.
Hope you are satisfied by this answer
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / sareer ahmad lone
Ans.First you have to find out the full load current of the
transformer that is IL=2915A then as per NEC you have to
give atleast 25% that is 2915x1.25=3643.75A.So the nearest
size of Circuit Breaker shall be 4000A.
Is This Answer Correct ? | 8 Yes | 6 No |
Answer / mukund
it is necessary to know what is the voltage rating of
transformer
many of the times 2000 kva x'mer are 22/11 kv less than
that are generally 22/0.415kv or 11/0.415kv first you
clear that
Is This Answer Correct ? | 8 Yes | 6 No |
Answer / foolinla
The capacity of a transformer depends on its rated voltage
and current. The load current varies depend on the voltage
of the transformer.
If this 3 phase 2000KVA has a primary voltage @ 4160V, then
the primary current is 278A (2000000/1.73/4160V)
If the secondary of this 2000KVA is 480/277 then the
secondary full load current is 2408A (2000000/1.73/480).
If the secondary of this 2000KVA is 208/120 then the
secondary full load current is 5558A (2000000/1.73/208).
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / aravind
WHile selecting any Circuit breaker the transfoemer rating
and Impedance should be considered.
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / khadu ali murthuja
Transformer rating already given=2000KVA
Select Air circuit breaker ie secondary current multiplying with 1.6A to the rating of the transformer.
secondary current = 2000×1.6
= 3200A Air Curcuit Breaker Required.
since 1KVA =1.6A
how to find out primary current.
the relation ship between voltage and current.
V2/V1=I1/I2
415/11000=I1/3200
I1=120A...
Is This Answer Correct ? | 0 Yes | 1 No |
WHY POLARITY TEST OF CT IS VERY IMPORTANT IN SWITCHGEAR
If two transformers same rating(11KV / 440V)connected in the same primary line(11KV), can we connect(bus coupler) secondary side directly or need a synchronization????
Dear Friends, Need your help for connecting APFC panel, Quotation : I have 2 No’s 1000 KVA Transformers, both transformers are having separate APFC panels, ( Tr-1,400KVAR, TR-2,450 KVAR) Now I want to stop One transformer, present load is 650Amps, Max, So One transformer is enough, I have switched OFF TR-1, but PF is not maintaining properly, its 0.5, So now I want to connect TR-2 APFC also in TR-1 Loads, Can any one answer for my Quotation with drawing, how to connect TR-2 APFC panel in TR-1 Loads,
how to check a transformer insulation?
3 Answers Kirloskar, Kirloskar Chillers,
why the insulators are in cofee colour???
A motor running with lenze frequiency inverter stops if I REDUCE SPEED with 25% load.If I run it in High speed and medium speed running smoothly with full load.please help me to solve it.
This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/11kV three phase star - star power transformer. The neutral was solidly connected to the earthing mat. But because of high resistance of earthing mat (130 ohm on LV and 180 ohm on HV), one day LV side neutral earthing conductor melted and we had a huge damage. Can any one plz tell me what might happen when we connect power transformer neutral to the earthing mat which has high resistance (>100 ohm ) ?????
how to test a motor from megger
The unit of resistivity is:(a) ohms(b) ohm millimetre(c) ohm metre(d) ohm/metre
what is entropy?
How to test lightning Arrester?
How to do the meggering for a cable.