Generally in AC we consider voltage, frequency and phase
sequence for parallel operation ... Can we parallel two DC
battery chargers? If yes, then what precaution to be taken
when we parallel two DC power?
Answers were Sorted based on User's Feedback
Answer / vijaykumar shetye
1) Yes, theoretically, we can parallel two DC battery
chargers, but generally they are not designed for parallel
operation.
2) Following factors are to be considered.
1) The voltage of both the chargers should be the same.
2) Both chargers should be connected in the same
polarity.
3) The output impedance of both the chargers should be
the same, so that both deliver equal current. (It is not
necessary that both the chargers should be of the same
make. It would rather prefer same model than same make.)
4) The characteristics of both the chargers should be the
same. Both should be set at the same current setting for
changeover from boost to float.
5) The current capacity of both the chargers should be
the same.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / pankaj verma
Main criteria for parallel connection is :
1. Both chargers should be connected in the same polarity.
2. Voltage of both the chargers should be same.
3. chargers should have identical specification.
Practically chargers are never used in parallel, they are
just momentarily paralleled in order to shift load of each
other so that maintenance work on each one can be carried out.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / omkar
) The voltage of both the chargers should be the same.
2) Both chargers should be connected in the same
polarity.
3) The output impedance of both the chargers should be
the same, so that both deliver equal current. (It is not
necessary that both the chargers should be of the same
make. It would rather prefer same model than same make.)
4) The characteristics of both the chargers should be the
same. Both should be set at the same current setting for
changeover from boost to float.
5) The current capacity of both the chargers should be
the same.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod
DC battery charger is feeding the float& DC load curent,
when AC fails battery will feed the DC,if charger fails
another charger can put in service.DC battery chargers not
required to parallel.(ie. battery having C10 capacity 100
AH or more)
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ramprasad
Before parallel operation of two DC Battery charger
precaution to be taken is
1. Both Battery charger must to be same make.
2. Output of Battery charger output must to same volt.
3. Primary of both charger must to be connected in parallel
with same phase sequence.
4. Output of Charger connected in parallel with same
polarity.
5. Voltage regulation must be very perfect of charger.
Is This Answer Correct ? | 5 Yes | 8 No |
Why P.F(power factor)relay should not be connected to the D.G(diesel generator) incomer side
How to calculate the KA rating for a circuit breaker if we know the KVA rating of the generator feeding it?
how to mesure the earth pit value and what is the minimum value of single earth pit?
Why a tesa lamp is glow between two phase?
What is Wlak Test in Fire Alarm System????
what is the differences between microprocessor and general purpose computer
Please brief what is sinewave
If a motor of 30KW rating &200 mtrs distance from feeder give me the cable size selection calculation?
what is the difference between a frequecy converter and an electric inverter?
Why are use 22 kv 3ph supply ?
FEINGING DECREASES THE FLUX DENSITY IN THE AIR GAP. HOW?
How will I know that how many batteries I should connect to my UPS unit?