1. how much normal earth resistance in earth pits(neutral
and body earth) and transformer neutral and body earth &
panel earth.
Answers were Sorted based on User's Feedback
Answer / rr0505
Earth resistance of earth pits shall depend on the terrain
in which the same is provided. Accordingly, based on soil
resistivity data of the location, no. of earth pits is
determined to ensure Grid earth resistance value below 5
Ohms for electrical grids,
For solidly grounded neutral of transformers, resistance
between Neutral & Body earth as well as panel earth shall
be zero.
Is This Answer Correct ? | 124 Yes | 24 No |
Answer / rvg.msceb
The earthing resistance indicates the easiness of providing
a path. It should be as low as possible. Different
countries having standard values. In india, for commertial
applications its <1 ohm, and for railway its< 0.5 ohm.
for air craft and ships temp. earthing <10 ohm.etc.
Is This Answer Correct ? | 82 Yes | 8 No |
Answer / shri6181
even any earth pit is concidered every earth pit should have the value 0ohms.but in rare cases u will get that value,more over will come 0.3to 0.9,there fore the earth pit value should be less than 1 ohm.ok
Is This Answer Correct ? | 68 Yes | 9 No |
Answer / sanjay
NUETRAL&EARTH BETWEEN VALUE IS 0. AND TRANSFORMER BODY
EARTH AND NUETRAL BELOW 1OHM,ANDRESPECTIVELY PANEL EARTH
ISALSO BEBELOW 1OHM.
Is This Answer Correct ? | 76 Yes | 38 No |
Answer / rakesh
For grid resitance it should be less than 5 ohms and for
indipendent earth pit it should less than 2 ohms.
Is This Answer Correct ? | 51 Yes | 42 No |
Answer / kalpesh
earthing resetens 1 ohm to 3 ohm in rainy sesion only 1 ohm &other sesion aprox 3 ohm
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / kalpesh
Earth pit resistance 1.4 TO 1.6 NORMAL CNDITION
Is This Answer Correct ? | 11 Yes | 6 No |
Answer / nandakumar.r
Earth pits resistance was 0 ohms.due to soil difference its
vary slightly near 2 ~ 3 ohms.But its acceptable level in
our country.
For transformer neutral and body earth and panel resisteance
was zero ohms.
Is This Answer Correct ? | 13 Yes | 10 No |
What is class 2 coordination ?
what precautions to be taken while desigining a LT,HT panel. Eg-LT panel PCC panel with ACB installed. HT panel VCB panel with VCB installed. & what is main diffrence betwn IP54 & IP55 construction of panel.
whats happen if we disconnect the NGR of alternator in running condition?. Generally we observed that transformer netrul is directly grounded but alternator connected with NGR, then ground?
What are the maximum and minimum ratings of MCB,MCCB,ACB,OCB,VCB and SF6 breakers?
2 Answers ABB, SK E&C, Sodexo,
why transmission voltages are in multiple of 11kv?
In winter we seem lightly an electric shock when we touch to doors(sometime)
What should be setting for alarm,tripping and cooling fan on for power transformer's oil temp. and winding temp. indicator?
why transformer do not rotate?
in 33kv/11kv stepdown t/f why should we use Star point
what do you mean by every IC 74 first digit.why are you using this no.why not using another no.
What is the difference between a Junction Box and a Marshalling Box?
A 12.5 hp slip ring motor taking high initial current and its MPCB is getting open.what may be the reason?