HOW TO FIND OUT 1. LINE CURRENT, 2. PHASE CURRENT IN AN
ALTERNATOR / TRANSFORMER WHICH IS FEEDING A I)STAR LOAD ii)
DELTA LOAD, USING A CLAMP METER.
NORMALLY WHEN WE USE CLAMP METER IN A DG SET THEN WHAT DO
WE GET?? PHASE CURRENT OR LINE CURRENT.
Answers were Sorted based on User's Feedback
Answer / debasish das
we can not measure phase current in three phase suply. if
we measure the current that will be the line current .and
if we devide this current by .732 then we will get phase
current
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / rahul
u can find the phase current from the CT out going. then u
calculate the line current herewith
Is This Answer Correct ? | 3 Yes | 6 No |
Answer / vivek
dear sudheer, the question was to find it out practically,
as i wrote, using the clamp meter ..... theory we all know
but thequestion is how to apply the knowledge .... let me
ask the question in a different way..... where exactly
would u put the clamp meter in order to measure the line
curren and phase current?? because phase current passes
through the neutral and the line current through two
phases. .... so i guess one might need to open theload or
the source especially in order to measure the phase
current ....if anybody knows a link from where i can get
practical knowledge like this then pl let me know....
thanks.
Is This Answer Correct ? | 6 Yes | 11 No |
What is LT? And specify the range of voltage?
in 220/132 substation in place of PT what equipment used & what r the role of that equipment
What is the Diesel consumption between 82KVA DG Set and 180KVA DG Set for 1 hour.
Scott connection is used for A 3-phase to 2-phase conversion B to achieve higher effciency C to save copper D to reduce harmonics
if two heater of rating 1KW,200v are connected in series 100v supply what will be the power taken
hi friends ,iam working as genset AVR service engineer in electrical field from past 2 yrs throughout india . i plan to shift in some other job without travelling in same field because i con't travel,i dont know what i do for that so please guide me what job is suited for me,how i can serch the job please anybody helpme iam totally confused
Procedure for conduting vector group test on power transformers.why it is conducted?
When we are working on transformer(132\11KV). we are going to isolate the transformer from both HV side and LV side. then we are applying grounding on both side. My question is that we required to isolate the VT which is still connected from secondary side.?
why neutral can not used in three phase motor connection?
how to check the insulation for motor using megger?
What is Diff btw MCP & MCB????
10 Answers Athena, Emerson, Suzlon,
what is earthing.how we make it,describe briefly.