hoe to test voltage restrained overcurrent relay?
Answers were Sorted based on User's Feedback
Answer / prasun bhaumik
First put normal PT supply and then increase the current up
to the pick up level and then upto 2 times of it then see
the time of operation.
Then keep the current at plug setting value , now decrease
the voltage gradually to see the minimum restraining
voltage at which the relay will start to operate
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shivani
can u tell me which paricular relay u are asking.
Generally all relay tested on two theory.
1.pick up value test
2.Pick up time test.
Is This Answer Correct ? | 0 Yes | 3 No |
1 HP = how many kw
Difference between PLC and SCADA ? What are merits & De-merits of PLCs ? What are merits & De-merits of SCADAs ?
In the formula : Knee point voltage = Burden X alf / class, Please inform what is alf? regards Shashidhar M.R.
how diside ct mf exmp.200/5 ct
I have 2 Nos of 2500kVA 33/0.415V cast resin transformers. How to decide on ampere rating of HT Panel? Also advise me how many panel RMG i have to consider whether 4 panel ok?
orifice sizing how done, checking & selection
Give me check-list for electrical preventive maintenance of machine tool.
Greeting to all members, How to calculate spill current when we have different ratio CT and Class for REF(Low Imp) I have 500/1A 5P20 @line side n 400/1A CL.X @ Neutral.
We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one 2000KVA T/R during operational hours while non- operational hous 1250 KVA T/R also used to reduce T & D losses. Similarly, 2 capacitor bank of 500KVAR and 300 KVAR also installed to balance reactive power. Now problem is around 1000 KW load PF is not maintaning 0.99 as 350 KVAR capacitor is in healty condtion. Now the PF is maintain 0.95 to 0.96.
What is ERD used in Elevators??
why dc exicitaion used in ac motor....?
what is magnetizing current test in power transformer