what we happen if 400 kvar cpacitor banks are on in manual
mode and there is no load on mains ??????????????
Answers were Sorted based on User's Feedback
Answer / vinod sharma
If the bamk is on mannual it will lead the voltage.
Due to this the power factor will cross the limit 1 and
with this losses will increase.
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / rahul shukla
VOLTAGE WILLL RISE AND ALL LOADS i.e motors ect. get
overfluxed as v/f ratio will be high
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ashok
power factor is leading and average power factor decreased
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / er. ankush miglani 9718151073
if all this happen the power factor increases from unity
and the supply is fed back to the system i.e. the load
becomes the source.
or
when capacitors charge to its peak value they will not get
any path to discharge and remains charged i.e. nothing will
happen.
or
practicaly try karne ka yaar.........
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / chandra
The load power factor becomes leading and load becomes
source and power is supplying to the system instead of
receiving.
Is This Answer Correct ? | 1 Yes | 3 No |
what is the meaning of transformer short circuit test?
Pls explain about full theory of salient pole generator?
Draw a SLD for main panel for school having connected load of 1200kw and emergency generator 200kw.also show the increase of additional load of chiller 225kw in the lv panel indicating meter postion size of transformer ,cables and capacitor bank.
WHAT IS DIFFERENCE BETWEEN idmt and instentanous relay? is idmt is used as back up protection or else?or when instantenous relay saturates IDMT will operate???
some meggers have three terminals. wat is the real function of the earth terminal?
can we use metering current transformer as protection current transformer if not why? & if yes why?
What is meant by TAN-DELTA test carried out in motors?
How many 2 ton window A/c can runs on a 125 KVA generator?
NOW A DAYS THE POWER SUPPLY IS VERY LOW.SO THE FLURESCENT TUBE LIGHTS ARE VERY DIM.IS THERE IS ANY WAY TO INCREASE ITS BRIGHTNESS?FOR EXAMPLE ANY CONVERTER,CONDENSER?
ABOUT AC GENARETORS AND MAINTANANCE AND TYPES OF GENARETORS
it is possible to rotate the DG engine dc starter with wrong polarity connections? why?
How much current does a motor take in no load condition?