why does chattering take place in ac contactors?
can it be avoided & what care does the manufacturer take to
eliminate this phenomenon????
Answers were Sorted based on User's Feedback
Answer / terence
low voltage or voltage drop will cause them to chatter.
Is This Answer Correct ? | 43 Yes | 9 No |
Answer / srij21
Apart from the above correct answer,chattering may happen
aslo due to the loose supply wire given to the contactor
coil and also on the coils magnetic effect.
Is This Answer Correct ? | 28 Yes | 11 No |
Answer / reshi
Chattering will occur when there is no perfect contact
within the contactor, when chattering occurs the two
contacts may get weld together.This may cause a danger when
it is required to open the circuit or required to stop the
motor from the remote option.Chattering may also occur if
the contactor is undersized w.r.t load current.
Is This Answer Correct ? | 24 Yes | 12 No |
Answer / korra
Can be either one of these;
1) Low voltage condition.
2) Improper armature alignment.
3) Broken shading coils.
Is This Answer Correct ? | 3 Yes | 0 No |
chattering occurs due to many conditions:
1. due to loose contact
2. dust contents
3. new product will not get contact very quickly but after some periodic operation it will be rectified.
4. under coil rating e.t.c
so major is no 4 & 2 this shall be taken care by manufacturer
Is This Answer Correct ? | 13 Yes | 11 No |
Answer / kyle
Chattering us usually due to a loose neutral.
Swap out all mechanical contactors with mercury contactors, and be done with it.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / bhanu dudhat
i agree with above answer and
also manufcture can add
sheded pole ring when it
design bcoz ac current flow
positive ok but naturle side
pick up not possible so and
thats reasen they add sedded
pole ring for continios hold
contactor.
Is This Answer Correct ? | 1 Yes | 20 No |
Answer / selvakumar
my opinion to buy schneider electrical contactor is the best one,,,,,,,,,chattering not occur in that contactor,,,,,,,,,,
Is This Answer Correct ? | 0 Yes | 22 No |
The normal highest generated voltage in India is a) 6.6KV b) 132KV c) 11KV
why generation of electricity in low value voltage
I want to do a mini project. Now I'm studying in 6th semis tor EEE Engineering.
what is difference between c-power & u-power air circuit breaker?
2 Answers Areva, IIT, Marine Electricals,
purpose of breaker contact multiplication relay?
In the diesel generator wihch type of power we can get it ? Like AC / DC
2 Answers Aditya Birla, Indian Steel, PTPS,
how can we judge the percentage of load on the basis of temperature differences readings between WTI and OTI in a transformer
what is breaking capacity
when generator of a power plant is not connected to grid , by increasing the mechanical torque speed of rotor increases but when it's connected to load instead of increase in speed current increases , why?
Is it required to do earthing in 2nd shop if earthed armoured cable is laid from 1st shop ?
can anyone please help me to find the rupturing or breaking capacity in KA of circuit breaker (MCCB,VCB,ACB etc) of HT and LT side of a distribution transformer...please help with detailed step by step answer...thank you
a 3 phase slip ring induction motor is wound for 4 poles on stator and 6 poles on rotor; when 3 phase balanced voltage source at 50 hz is applied to motor it will run at a)1500rpm b)1000rpm c)750 rpm d)zero rpm
13 Answers Essar, PSPCL, PSTCL,