ANS is star with neutral and delta.For harmonics effect to
be minimum we must provide a closed path for harmonics in
phases so that they circulate only in phases and does not
enter into line.Hence harmonic effect is less in delta
connection than in star connection.In star star connection
ti provide closed for harmonics neutral is grounded
| Is This Answer Correct ? | 1 Yes | 1 No |
what is the meaning of Ring Mean Unit in a substation or trasformer also tell me its oerpuse?
What it is the diff btw Package & PEC AC's????
11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?
formula for cable size calculation for current?
10 Answers KL Power, ONGC, RL Clean Power Pvt Ltd RLCPPL, SAS, Sobha Developers,
The DC current waveform is - . What about the fire alarm waveform?
what is corona ?
How to do cable sizing calculation for 750 A Neutral Earthing resistor for 33kv. the 33kv cable going to swbd. is 630mm2 3 runs.
Why Transformer Neutral having one earth pit ( more earth electrode resistance) whereas body have many earth pit ( less earth electrode resistance)?
Define open loop control system.
Transformer/insulating oil tester(BDV tester)
How to choose size of the cable w.r.to current carrying capacity ...
what is over cureent protection
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)