Answer / moody
of course
when load pf is constant and the load current increase the
t.v decrease " lagging p.f"
at leading pf the t.v increasing
this occurs in synch generators
if the load is constant but the p.f changed or varried
the same operation happens in lagging , leading respectivly
thanks................
Is This Answer Correct ? | 15 Yes | 0 No |
Answer / rahul
Yes it does.
Reactive loads ABSORB VARs. This may lead to deficit VARs
in the system causing VOLTAGE to GO DOWN.
( Note that EXCESS VAR___High VOltage
DEFICIT VAR___FAll in voltage)
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / ritesh
yes, when reactive load is changed, the load power factor is
also changed. line current= active power/(voltage*pf),
therefore line current will also change for a constant load,
which will change the line voltage drop, therefore terminal
voltage will also get change.
Is This Answer Correct ? | 1 Yes | 0 No |
Yes it will drop down vtg
increase in var can increase vtg
Is This Answer Correct ? | 1 Yes | 0 No |
yes,
when reactance increase loss increase
so voltage decrease
Is This Answer Correct ? | 5 Yes | 7 No |
What is center gravity load in substation?
explain the meaning of harmonic resonance
What is superposition theorem?
What is the differance between vacuum breaker and vacuume contactor
what is stepping motor and where can use in electrical installation.
what is the function of rccb how it diffrentiate between elcb
How can claculate to attain the desired PF in the line ( HOW Much KVAR is required ) Pls Give the formula?
What happens if fuse is connected to neutral wire
working principle of AC Servo Motor with its construction
What is the concept of voltage & current its relation?
why do we generate only 3ph ac?is it possible to generate 4ph,5ph,....?
6 Answers Accenture, Bhel, Reliance,
How many no. of earthing pits required for commisioning a new 320KVC DG Set????How????