for distribution line ratio of x/r
1.<0.1 2.>10 3.>1 4.<0.01
Answers were Sorted based on User's Feedback
Answer / shantanu mishra
x/r ratio is the ratio of reatance of the line and
resistance of the line. In distribution lines like 400 volt
three phase line, the resitance is far high than reactance
or we can say the reactance is negligible as compared to R.
Therefore x/r ratio of dist.line is less than 0.01. for
11kv line this may be less than 0.1.
THis ratio increases as we move towards high and Exta high
votage lines.
| Is This Answer Correct ? | 29 Yes | 8 No |
Answer / sandeep
X/r ratio for distribution line is more then unity
| Is This Answer Correct ? | 19 Yes | 7 No |
hoe to select the cable size in sq mm for certain load?
What are the complete specifications of a motor?.
why supervision relay is used in incoming feeders?
In india the power supply is always in multiple of 11, eg.220 V, 440 V... what is the reason?
11 Answers BSES, Electrical, L&T, PSIT,
What is difference between stable and steady?
describe the Tranformer testing procedure
For 7.5kw star delta starter how to calculate 1. Mccb rating 2. Contactor rating 3. Over load relay rating
difference b/w eath and neutral
How to set a Zone 1 distance relay for distribution feeder?
0 Answers Schweitzer Engineering,
What is the relay function?
what is per unit calculation?looking for simple and strong explanation thk u
for a machine R=130 KVA Y=132 KVA B=144 KVA Then what will be the total kva
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)