How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can
u give me Answer.
Answers were Sorted based on User's Feedback
Answer / naren
connect to pressure calibator, apply the low pressure -60
adjust the span into low pressure and then apply the high
pressure then adjust the span screw into high value. it is
calibrated in the range of -60 to -20.
if it is the SMART transmitter its easy, just apply URV and
LRV value through Communicator then connect to the pressure
calibator then check URV, LRV and intermediate value
| Is This Answer Correct ? | 20 Yes | 6 No |
Answer / ramesh
we can apply the +ve pressure to the lp side that is 60
with zero, then +ve 20 with span with respect hp open to
atmosphere
or apply -ve pressure that is vaccum to the hp side with
respect lp open to atmosphere
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / welcome4ujd
make the calibration set up , to get -60 , give 60 in lp
sidethen adjust zero screw, give 20 in lp side toget -20
url , and adjust span screw.
| Is This Answer Correct ? | 18 Yes | 12 No |
Answer / sn
apply -60 to the transmitter n make the o/p as 3 psi, then
giv -20 as the input n adjust the o/p as 15 psi.
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / sandeep patel
connect transmitter in bench setup, left LP side of transmitter open to atmosphere and apply -60 mmwc to HP side and check it s o/p is 4 mA or not and if it is not, then do zero trimming. then apply -20 mmwc to HP side and check o/p is 20 mA or not otherwise fo span trimming.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suresh agravat 83204 78125
Urv-LRV÷4=Span
-60=4ma
-50=8ma
-40=12ma
-30=16ma
-20=20ma
Apply pressure accroding to above chart and monitor output
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / anup ramteke
It depends upon the type of transmitter u are having. If its
HART based transmitter then either u can calibrate it
through HART calibrator. firstly go to basic set-up mode and
feed the URV as well as LRV values. And if u want to
calibrate it at field itself when HART calibrator is not
available then u can set LRV value by entering its value in
mode 2 whereas for URV its mode 3.
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / suvendu sekhar giri
You can give positive pressure on low pr side keeping the
high side open to atomosphere for lrv (-60) & urv (-20)or
you can give negative pressure on high pr side for lrv(-60)
& urv(-20) keeping low side open to atomosphere.You can
adjust zero at lrv & span at urv. If it is smart
transmitter then you can zero trimming keeping both the low
& high pressure side open to atmosphere.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / venkat
actually we can calibrate LP side by positive pressure and
Hp side also we can calibrate by negative pressure but LP
side better
| Is This Answer Correct ? | 3 Yes | 7 No |
Explain the burnout feature.
why we use only 4-20 ma signal as AI and not 0-20 ma?
2 Answers Honeywell, Oil and Gas Jobs,
what is a good line as ic engineer as maintenance ,oc, project, calibration ,validation engineer?
I heard that we can use flow transmitter for level measurment also hw it is?
what is the well head protection system?
how can calibrate transmitter online
how to make a calibration for differential pressure
what is the use of conrol cable..?
What are the materials use for COntrol Valve body?
1 Answers KNPC, Qatar Petroleums,
Isometric drawings are generated during _________________ phase of a project
If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used?
Hot calibrate a level transmitter (wet & dry legs)?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)