Answer / mahesh bial airport
Transformer testing is mainly two type because calculating
the losses of transformer 1) open circuit test 2) short
circuit test. In opencircuit test showing hystorisys
loss ,eddy current loss ( magnetic loss ). In short circuit
test showing copper loss of the transformer
Is This Answer Correct ? | 19 Yes | 0 No |
Answer / bimal
Transformer testing is mainly done to know the correctness
of wdg,core, etc.....
The Lv tests are.
Vector Group,Magnetic Balance,Magnetizing Current,Ratio,
Hv test are.
Impulse test,switching,etc.
Is This Answer Correct ? | 9 Yes | 2 No |
Answer / venkat
Transformer test are,
Insulation Resistance Test,Voltage Ratio Test,Magnetic
balance test,Vector group Test,Magnetising Current
test,Short Circuit Test,Oil Test
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / dany
Basically transformer tests are of two types.
1)short ckttest 2)open ckt test
short ckt test gives us 1)copper losses 2)voltage regulation
3)lekage impedances(ie. resistance and lekage reactance )
open ckt test gives us 1)core losses 2)parallel component
values (ie Rc and Xm)3)secondary voltsge
Open ckt test will be done on lv side ,while short ckt test
will be on high voltage side
Is This Answer Correct ? | 6 Yes | 4 No |
i want to learn control schedule for 11kv panel? can any one send the detailed control schedule?
Why do we require transformer with less specific weight if supply frequency is increased?
Why the resistance grounding (NGR) is better than Solid grounding?
difference between moore and mealy model
We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11KV switch yard having 12.5MVA power transformer. Some times we draw power during emergency. It is observed that during Export or Import for load less than 500Kw the power factor is decreasing to 0.3 . This is happening only during export or import. During island condition TG power factor OK.Our capacitor bank is provided with our Power plant auxilliary load. Please suggest how I can we improve our power factor during low load (GRID).
What facility we get after CT secondary earthing and how?
what is relay multiplier
1 Answers Atomic Energy Commission, Bhel, Wipro,
derive the formula of amp hours is calculated for 12v battery.where no. of plates is given
why induction motor always operate at lagging p.f.?
explain all the classes with example
How is operate breaker failure scheme in substation
Why is it not possible to operate a star-delta transformer in parallel with delta-delta transformer?