Comparative difference between 33Kv & 66KV for transmitting
the load of 7 MW at a distance of 34 Km.
Answers were Sorted based on User's Feedback
Answer / kapil
transmitting through 66kv is better than 33kv because losses
in 66kv is less as compare to 33kv line.
| Is This Answer Correct ? | 46 Yes | 7 No |
Answer / bharat kanojia
As losses are inversly proportional to square of 'v'.
therefore 66kv could be a better option, but as the line is
a short transmission line,cost factor would come into
picture,hence accomodating everything 33kv is the most
fitting.
| Is This Answer Correct ? | 24 Yes | 5 No |
Answer / ayush
1.as voltage of line is increased current is decreased.so
the copper losses associated wth current r reduced.but iron
losses dependent on voltage r increased.as the supply
voltage is constant so r the iron losses.but copper losses
vary wth load(load current)bcz current is less we cn say
that overall losses i.e. cu nd iron losses r reduced.
2.as nw supply votlage is increased size of current
carrying conductor reduces as current is low so less area
required for power dissipation.
3.as losses r less so higher is the effiency of line so is
the power transmission capability.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / shafiq
if there is short trasmission line it has negligible
inductive losses. there4 v prefer 33kv trasmission for this
load & order to save capital cost of the system.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / ganesh9703840484
7mw load is huge load.to travel 34km it is come under
medium transmisson line.so it is necessary to reduce the
losses. if the voltage is high current becomes less.so
copper losses are reduced.so 66kv transmission is preffered.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / r k gupta
You have to find break-even cost for capital expenditure and running expenditure for both 33 and 66 kv system. Optimise the load at which 66 kv system survives the capital cost. It's simple
| Is This Answer Correct ? | 0 Yes | 0 No |
why solinoid coil used in tripping rely?and why not other type coil?
how "rabbit ACSR" conductors are more efficient than "weasel ACSR" conductors
which model T or pie model is prefarable in power syatem
In transformers Which type of connection is preferred for harmonics to be minimum. primary : secondary star without neutral:open delta star with neutral :open delta star without neutral: delta star with neutral : delta explain why
please send me jindal previous aptitude and technical question and answer.my email id is deep_raj@live.com
in a distribution board,if we have a load and we have selected a cable after making all calcs (Deratings and V.D , ect...) the cable we have selected was 10mm.sq. now, shall the internal cable inside the switchboard should be 10 mm.sq Like the external or it can be Less???? if somebody have an specs or information he can help D:
Mathemetical Relation Between KWRH and KWH?
In sub-station how to find multifactor of panel?
in transformer which grade oil will use?
A double circuit with dog conductor 66KV Transmission line from wind farm evacuation to feeding substation having capacity of 25MW for transmission. Can same transmission network be considered for further expansion of Power & how much in MW. If we need to expand next 10-15 MW more will there any augmentation is required in transmission network? Kindly reply asap.
How many watts required for single phase power supply?
Explain why the Voltage drop will happen in 3 Phase line?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)