which is batter in construction job,ELCB or RCCB?

Answer Posted / pravesh badoni

elcb as the name suggests earth leakage circuit breaker.
while rccb is residual current circuit breaker. any current
which remains in circuit disturbs the operation of machine
and is harmful for the ckt.rccb and elcb both are the same
thing which satisfies the purpose of disconnecting the
circuit when any residual or leakage current persists in
the circuit both are rated in milli ampers ranging in
fractions of ampere (30 ma to 80 ma).

Is This Answer Correct ?    7 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is the minimum value of hfe for the oscillations in transistorized rc phase shift oscillator?

769


how single phase preventer works ?

2019


Write down the name of 2 lady Bir Pratin of Bangladesh

1469


which capacity of RCCB used for five thousand watt electricity load?

1349


The moisture in air will condense at

681






how much excitation voltage required to generate 1mw power?

1603


What is the exact minimum vale of voltage between an earth and netural which can damage or can do malfunction of the electronic equipments ? If this is mentioned in any book, pl.give reference.

1815


What do you mean by a phase angel of instrument transformer?

642


What is center gravity load in substation?

1939


What is the difference between solid grounding and impedance grounding?

1542


what is meaning of bus riser

1950


how to calculate the fault in substation

1721


wat is meant by PX class in ct?

1576


kVA rating of ordinary transformer is increased when connected as an auto transformer because A transformation ratio increased B secondary voltage increased C energy is transferred both inductively and conductively D secondary current increased

2155


what is the profesional board for electrical engineer what is thepast and during construction for electrical engineering

1466