why we use star connection on the primary side of a
transformer?
Answers were Sorted based on User's Feedback
Answer / habib
Transformer primary is not in star we can say for all
transformer HV side should be in star,because in star Phase
voltage will be reduced by 1.732 times to delta,so it
reduces the insulation requirment.
Second in Generating station transformers load side that
means the side which will be connect to the grid will be in
star,because grid distubances should not circulate in
transformer if it is in delta distrubances circulate in the
transformer which reduces the transformer performance
Is This Answer Correct ? | 58 Yes | 7 No |
Answer / niranajn
since the phase voltage for star connection is 1/sqrt3
times of line voltage the insulation required is less .So
the primary side is star connected
Is This Answer Correct ? | 19 Yes | 4 No |
Answer / rakesh
in star connection the phase voltage is reduced by 1.732
times than the line voltage, since the voltage is reduced
the insulation required in the winding of the transformer
also reduces.so it economical to connect the primary side
of the step down transformer i.e the hv side,in star
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / mukhesh
we cant tell always primary is star depend on riqiements
because at genareting station lv side is connected to
station and see side should be star bcz step ujp the
voltage and disubutuin side lv side always seec side is
star bcz it has nutral
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / santosh
Always HT volts are the out put of a EHV transformer which is Delta-Delta connection.But in general Distribution transformer,We have HT(11kv) primary side and LT(415v) secondary side. So 11kv should be Connected with delta connection and 415v should have star connection.
Mainly LV/2ndary side connected to home appliances,which is running with 1-phase and 1-neutral.
Is This Answer Correct ? | 0 Yes | 0 No |
Can I use star delta connected induction motor for dual supply voltage?
what is meant by unity power factor?unity means one why dont call 2,3,4......?
how will you determine the short circuit capacity of a network
how capacitor active and reactive.
how to select diiferent power transformers of same capacity on no load loss and full load loss by economical point of view.?
If 3-Ph motor of same rating connected in Delta & Star for same load one by one then which connection take more current in running (not in starting)for full load.(eg 8.5 KW,3-Ph 400 V)
Can we use a window type neutral CT instead of a bar type neutral CT. We have an issue with a neutral bar type CT of 800/1 ratio with a Circuit breaker NS800L shneider type, and we want to change it with a window type. Pls advise. Thanks
What is Isolation Current transformer and what purpose to use it in REF relay ?
How many types of AC current?
sir, 3phase induction motor takes different pf and different KW in three phase while running,explain reason
difference between relay and solenoid?
if single phase is having 220v supply then why three phase is having 440v instead of 660v?