How to calculate KW what is the formula for KW.
Answers were Sorted based on User's Feedback
Answer / pankaj kumar vig
IN SINGLE PHASE
POWER= V*I*COS $/1000 KW
IN THREE PHASE
POWER=1.732* V*I*COS $/1000 KW
| Is This Answer Correct ? | 53 Yes | 9 No |
Answer / dnyaneshwar
for single phase
KW= V*I*COS $
FOR THREE PHASE
KW= 1.73*V*I*COS$
IF U HAVE TO FIND ONLY WATTS THEN DIVIDE THE ANS. BY 1000
| Is This Answer Correct ? | 26 Yes | 8 No |
Answer / manik chatterjee
KW=V*I*COS$ THAT IS INCASE OF AC.
KW=V*I THAT IS IN CASE OF DC.
| Is This Answer Correct ? | 16 Yes | 0 No |
Answer / manik chatterje
IN CASE OF SINGLE PHASE AC
KW=V*I*COS$
In case of three phase
KW=1.732*V*I*COS$
In case of DC
KW=V*I
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / uzair ahmed
To calculate value in KW, just multiply the power with 1000.
becoz unit of power is Watt (W)
so if we convert it to KW then we mutiply it with 1000.
again if we convert KW into Mega Watt. we shall multiply
the value which is in KW to 1000.
and for low values that is maga watt to KW or KW to W, we
shall divide that values with 1000.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / poka
3 phase
________watts___________
voltsxampsxPFx1.732
1 Phase
___________watts______________
voltsxampsxPF
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / edgar
KILOWATT (kW) = VOLTS x AMPERES x POWER FACTOR x 1.73
---------------------------------------
1000
| Is This Answer Correct ? | 16 Yes | 10 No |
Answer / pradip ramoliya
Watt = ampier x volts and 1kw = 1000watt
| Is This Answer Correct ? | 13 Yes | 8 No |
What are the effects of armature reaction on a DC machine and discuss the various methods to reduce the effect.
plzzzzzzzzz plzz send me the papers of JSPL WRITTEN TEST..SO that i can prepare for the test in electrical engg..
how we can select MCB ratings according to Voltages, Curves.
What is the simplest formula to calculate the rotor diameter of a synchronous generator?
A 100KVA SINGLE PHASE TRANSFORMER 10000/200V,50HZ REQUIRES 300V AT HV SIDE TO CIRCULATE FULL LOAD CURRENT WITH LV SHORT CIRCUITED.THE INTAKE IS 1000W.THE % OF REGULATION ON FULL LOAD AT 0.8 PF LAGGING WILL BE HOW MUCH AND THE SECONDARY TERMINAL VOLTAGE ON 0.8 PF LEADING WILL BE
Draw an S.L.D of the main panel for a hospital, showing meter position. Essential loads are: 1) Equipment load 100 KW 2) Critical load 500 KW 3) Life AID Safety load 400 KW 4) NON-Essential load 200 KW 5) Other service loads 200 KW Calculate and suggest the size of the transformer, size of main cable, capacitor bank, and calculate the capacity of an emergency load having above first three mentioned loads is supplied by an emergency generator.
how to calculate compresor capacity?
can transformer develop three phase poer from a single phase source?
what is the principle of operation of domestic fan?? what is the role of capacitor in it??
How can you calculate in detail the VA burden of current transformer used for Restricted earth fault protection? Please understand that the CT required here is Class PX or X. Also please show the calculations for knee point vtg, stabilizing resistor, magnetising current.
what is meant by armature reaction & where its happen ?
what is the purpose of commutator in DC motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)