how to check the earth resistance value& what is the
minimum earth resistance for good earthing sysytem.
Answers were Sorted based on User's Feedback
Answer / jaydeep parmar
value of the earth pit should be less then 2 ohm and earth grid value should be <1 ohm
| Is This Answer Correct ? | 428 Yes | 59 No |
Answer / tauseef tarique, engineer(e)
The earth resistance value can be checked by the use of
earth resistance tester (called megger earth tester). The
best earth resistance should be less than one ohm but the
permissible value is less than 5 ohm. For rocky areas it
should be less than 8 ohms.
| Is This Answer Correct ? | 318 Yes | 43 No |
Answer / pandiyarajan
Grid resistance value should be lessthan 1 ohm
| Is This Answer Correct ? | 209 Yes | 31 No |
Answer / aruna devi
By using earth megger .It should be less than 2ohm.
| Is This Answer Correct ? | 227 Yes | 72 No |
Answer / bhavini
earth tester use for measuring resistance of earth pit
should be less than 1 ohm.
| Is This Answer Correct ? | 105 Yes | 26 No |
As such there is no any standard of earth resistance value,
Its varies on different type of soil resistivity. Idley it
should be 0, but in different kinds of soil for electrical
equipment it should be better to below 10 Ohms and for
electronic equipment it should be better to below 5 ohms.
| Is This Answer Correct ? | 100 Yes | 28 No |
Answer / ramaraj.g
The earth resistance value can be checked by the use of
earth resistance tester (called megger earth tester). The
best earth resistance should be less than one ohm but the
permissible value is less than 5 ohm. For rocky areas it
should be less than 5 ohms.
we using the DMM in check the L - N , N- E ,E- L
this small calc
L-N - 230 v
N-E - BELLOW THE 2 VOLTS IS GOOD ERATH CONN
E-L - 230v IS RECONFORM TO GOOD EARTH OR NOT
L-N = E-L
| Is This Answer Correct ? | 77 Yes | 11 No |
Answer / bk sharma
It should be near <0.5 ohm for good earthing.
| Is This Answer Correct ? | 64 Yes | 11 No |
Answer / bhanu
earth testers are used. and it is checked wheathe earh
resistance range is from 1-2 ohm or not.
| Is This Answer Correct ? | 83 Yes | 39 No |
I have c license but I don't know eligibility of Max Kilo Volts under the electrical licensing board.
Dear Sirs, I am a technical persons.In one of our Electrical Sub- Station, We have installed three numbers of 1250KVA ,11KV/0.415KV Transformer to feed the Factory load. We have found some abnormality. In one of our Transformers the leakeage current from transformer body to earth through earth continuity wire is almost 86 Amp but in other transformer it is (5-10)Amp. where the load current on three phase and neutral are respectively 1360Amp,1400Amp,1370 Amp & 176Amp. So please any technical person help me about the reasons of this situation and how I can rectify the fault. Moreover,I have measured the earth resistance of the Earth continuity wire which is less than 1 Ohm. Thanks Tapas Barua
What is difference between PVC cable & XLPE cable?
how to calculate power factor of capacitor? what is transformer rating?
what is diversity factor ? plzzzzzz describe me
why all selected supply voltages are multiple of 11.i.e440,11 kv,33 kv,66 kv,110 kv etc
how much importance of power factor in single phase. is it,s importance is quiet same as like three phase power system.
is the electrical energy photo copy possible or not???????????? give me some idea about that i m very great full tu u.
Explain the grounding concept adapted in aircrafts?
i want design of D.C.MOTOR 1HP 960RPM AND 2HP 960RPM ITS URRGENT
for leading power factor penalty by SEB why
which is dangerous AC or DC? If so why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)