expalanation for 5p10 class.
Answers were Sorted based on User's Feedback
Answer / anilesh
5p10
5% of error when there is 10 times of current in the
circuit.
Is This Answer Correct ? | 65 Yes | 6 No |
Answer / ravi kaslikar
5P10 means 5% composite Error up to 10 times of rated CT
current. 10 is for ALF ie Accuracy Limit factor. P
indicates Protection class CT.
Is This Answer Correct ? | 37 Yes | 6 No |
Answer / gopalsing
5P10,Means 5%(5P) Of Ration Error Even if 10 Times fo Rated
current pass through the primary of CT
Is This Answer Correct ? | 26 Yes | 4 No |
Answer / arun kumar
10 times of rated primary current injected means 5 percent of composite error is created .
5 - composite error .
P- protection.
10- accuracy limiting factor
these r the standard ALF list - 5 , 10 , 15 ,20 ,30
composite error is related to harmonics
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / grayghostgg
5p10means 5 percentage error and 10 mean ten times the
secondary current the CT can withstand
Is This Answer Correct ? | 3 Yes | 8 No |
Answer / bhanu
"5P 10" in this 5P Accuracy class,10 represents composite
error
Is This Answer Correct ? | 14 Yes | 30 No |
What is the difference between IGBT and TRIAC?
What is meant by Active and reactive power?
How to Calculate Stc Rating of an indoor type VCB Panel? What is a full form of STC?
During Starter Panel Com missing I Found The Main Incomer 40Amp MCB 10KA Trip When Motor Change Star To Delta Motor Rating 20HP BUT When We Use Same MCB To Other Motor It Does Not trip Or What Is Necessaries for Star Delta Starter MCB SFU MPCB OR MCCB And What are The Breaking Capacity of MCCB in the Motor above 15HP
what is the working principle of induction motor
why three phase system is not preferred in aircrafts power cckts if yes than explain reasons?
What is Scott connection? In which device it is used?
generally on the roadside v hav 11kv line which is being step down to 440v line to line....so any1 can tell me which type of transformer they r using whether it is star to delta,delta to star etc...???
Why the dc voltage drop during starting of emergency lube oil pump? The Voltage drop from 135kv to 125 kv for one min. before re-establish to 135kv?
how calculate kva in to kw
WHAT IS SUBSTATION & ACCORDING TO VOLTAGE HT,EHT SUBSTATION EXPLAIN IT
Frequency in the control system represents? Continuous system in time domain ? In frequency domain?