Answer / rukmagoud
Differential protection requires two cts for its connection.
If one of the CT reaches its Knee point voltage , then the
CT Enters into Saturation. so when Ct is in Saturation
state, its characteristic changes, i.e the current will
not be proportional to primary current thereby
differential current comes into picture in differential
relay , there by there is a chance of maloperation of relay.
This usually comes when there is any through fault.
rukmagoud
APGENCO/NAGARJUNASAGAR
| Is This Answer Correct ? | 49 Yes | 1 No |
Answer / ramesh p
the differential relay will get maloperation when one of
the CT get saturation
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / girish kumar samal, hindalco,h
DIFFERENTIAL PROTECTION FAIL. CT DOES NOT GIVE SECONDARY
CURRENT ACCORDING TO PRIMARY. EOR WHICH DIFFERENTIAL RELAY
OPERATE.
| Is This Answer Correct ? | 12 Yes | 8 No |
Answer / tony
Normally the knee point voltage must be
Vk > 2*Vs
Where Vs is the calculated max. voltage appears across the relay.
Beyond knee point the chara of CT is no longer proportional to the primary current and this cause faulty measuring by relay.Thus if we have higher Vk we can easily with stand higher Vs(fault equivalent seen by relay)
| Is This Answer Correct ? | 0 Yes | 0 No |
HOW TO CALCULATE THE CABLE SIZE FOR POWER CABLE, CONTROL CABLE AND INSTRUMENT CABLE
in 5 mva transformer 33/11 kv s/s what rating of capacitor bank is required & what is the fourmula for rating
how do you select the ct/pt rating in substation
1 Answers Apollo, Shreem Electric Ltd, Tata Motors,
the resistance of wire having length X M is R OHEM if i streched the wire to dubble length what will be the resitance
why the protection turbo generators is most complex?
why we are using2 wave trap in a feeder?
ful form of gis
why current flow throgh conductor.
Why the design of electromechanical energy conversion machines is based on the medium of conversion as megnetic field not as electric field?
why transformer ratings in kva?
99 Answers Bhel, College School Exams Tests, DOW, Emco, Esab, GE, KCP, PGCVL, Sodexo, TCS, vtps, Wipro,
which circuit breaker enclosure is best for maintenance guy? 16 bolt & 20 bolt squre or 16,20 bolt hinge
my 10 hp submersible pump is tripping when connected through ELCB.I have checked the megger value of the coil's with body.It was found to be 0.2mega ohm.that is leakage is there.But when connected to mccb it is not tripping.no leakage current in the motor.Is it safe to connect to mccb? what are the problem's will arise if future?also tell me in ELCB no neutral is connected to motor.than how ELCB was working?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)