my 10 hp submersible pump is tripping when connected
through ELCB.I have checked the megger value of the coil's
with body.It was found to be 0.2mega ohm.that is leakage is
there.But when connected to mccb it is not tripping.no
leakage current in the motor.Is it safe to connect to mccb?
what are the problem's will arise if future?also tell me in
ELCB no neutral is connected to motor.than how ELCB was
working?
There may be a minor leakage in , also please check the
mAmp of the ElCB if it is 100ma then there is a possible
chance of tripping on minor leakage.. i suggest you to try
with 300ma ELCB even if get tips then you have to check the
motor winding & connecting cable thoroly.
Is This Answer Correct ? | 9 Yes | 1 No |
what will happen if a 3 phase motor is connected to a single phase circuit and vice versa?
how we explain parallel paths armature winding?
in which direction real power and reactive power flow and why???????
Dear sir,We have a 7.5hp motor,it was running smoothly and suddenly one winding is carring more current then others(r=6.5,y=6.3,b=10)..whts wrong with tis...?
how to set relay setting? and example calculation...
can we identify the direction of power flow in transmission line by after only looking the tower
7 Answers TNEB Tamil Nadu Electricity Board,
explain why the armature voltage changes when the field rheostat is varied in self excited DC generator
why dc is used in control circuit for mv & hv switchgear instead of ac
why do we earth the tandelta point of a power transformer bushing?
lightning arrester rating selection procedure: (line to line voltage(kV)/(squ.root of 3))*squ.root of 2. now the question is, IS this above formula correct for both STAR and DELTA connected system???
what is RR number Abbreviation energy meter
why core losses are affected with change in voltege in transformer?