if we convert kw into Ampers,which one formula use by
us,pls tell me?
Answers were Sorted based on User's Feedback
Answer / sandip
In Dc supply we just divide by voltage and in AC supply we
divide with voltage and Power Factor depending upon non-
linear load
| Is This Answer Correct ? | 20 Yes | 4 No |
Answer / k.jagadeesh
In DC supply. kw/voltege
In AC supply (3ph)= kw/ 1.732xVxPFX Efficiency
In AC supply (1PH) kw/v
| Is This Answer Correct ? | 15 Yes | 3 No |
Answer / sameer
First covert kw to kVa kva = Kw / PF(0.8)
Rated full load current in A = (Total connected load in
kva / sq.rt * 3 x Supply Voltage) x 1000
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / jaimin
FOR 3 PHASE CKT
KW=ROOT(3)*V*A POWER FACTOR
A=KW/(ROOT(3)*V*POWER FACTOR)
FOR SINGLE PHASE CKT.
KW=V*A*POWER FACTOR
A=KW/V*POWER FACTOR
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / harish
KW is always a real quantity and hence we do not
require any power factor term...simply divide he given kw
by the voltage and you get the required amperes...
| Is This Answer Correct ? | 14 Yes | 20 No |
Answer / riyadh
we know load watts , u apply below formula for 3 phase &
single phase
3 phase I = Total load in watts/3*220V
1 phase I = Total load in watts/220V
| Is This Answer Correct ? | 3 Yes | 11 No |
what is AVR and tell principle and working?
10 Answers ITC Infotech, MIOT Hospitals, YCC,
for 750 kw LT load what will be the ht kva
What are the consequences in using existing step up transformer (primary 6.6kv/175A, secondary 480v/2405A) for step down transformer to have a 6.6kv output?
What are the two segments of nyquist contour.
Salient pole alternator is more stable, why?
sir i have a car stereo system and there is jack on him so can u tell me a way to find out their power terminals on the jack or on the circuit board"
How the power factor is more in high speed machines
How to calculate KW saving for power factor correction from 0.92 to 0.98 at 350KW load?
IS HI-POT TEST DONE ON A TRANSFORMER - YES OR NO? WHY?
I have 30 kw motor load & i have selected 10 kvar capacitor bank for power factor improvement.my existing p.f is 0.85 & proposed p.f is 0.99 so ,is it right selection? 2 nd question how to connect c.bank whether in delta or star connection & how to decide it?
What is thef ormula to calculate the rating of a capacitor for a single phase motor
PLC Training in chennai | PLC Training institute in chennai, PLC Training center in chennai | Best PLC Training in chennai | PLC Training course in chennai | SCADA Training in chennai | PLC Training in india
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)