How do determine the Size of a Droop Current Transfomer for
Paralleling of Two Generators, Say I need a Droop Current
transformer for a 600 kW generator need to be parallel with
a 800 kW generator, etc.
Answers were Sorted based on User's Feedback
Answer / satish babu
Consider two parameters to descide the CT ratings,
a) Primary current on the phase is 1050 amps,Consider No of
leads it has from the generator - If one cable is connected
your primary can be 1000A-1200A
If two leads are used , use only one lead as CT primary
then the CT primary can be 500-600 A
b) Your secondary can be 3A / 1A / 0.5A depending upon the
AVR used
Is This Answer Correct ? | 8 Yes | 3 No |
Answer / r.nombri
Haven't really used a Droop CT. Droop is the decaying of
current from it's initial peak/input, so your trying to
maintain synchronism of two generators in parallel with a
droop CT. By which the Droop CT may be used to improve the
secondary output connection between the two generators with
respect to their rated VA, and kW.
R.Nombri
Is This Answer Correct ? | 0 Yes | 5 No |
What are the maximum and minimum ratings of MCB,MCCB,ACB,OCB,VCB and SF6 breakers?
2 Answers ABB, SK E&C, Sodexo,
1 ph induction motor winding priniple and connection diagram?Similarly for 3 ph induction motor?Full description
How many types of Transformers are there?
what do you mean by plant earthing system.
Can anyone explain how the vector diagram of a transformer which doesn't have name plate be found whether it is Dy11/Dy5/Yd11 and so on?
why+ve is earthed in electrostatic precipitator in thermal power plant
Is it possible to run HT motor through LT VFD (LT VFD supply given to Transformer LT side and transformer HT side connected to motor)
what iz second and fifth hormonics please explain
please send me last 5 year interview questions
What kind of maintenance is conducted for generator
how to remover corona effect and hysteresis losses from contactor
During the main stator winding insulation testing (phase to ground)of 11kv alternator (Lerysomer) i found 0 and resistance with multimeter and found 20 killo ohm while the power cables are connected both end (Generator & VCB). In VCB PT (Potential transformer) are connected. Please any body explain that method of insulation is correct or not? also describe of PT connections