Answer / krl raju

If alternator voltage is considered 415 V, then rated
current of the Alternator is
=500*1000/(1.732*415)=695.6Amps.
Hence we need to select the neutral conductor to withstand
the half of the full load current i.e 350Amps


Is This Answer Correct ?    9 Yes 2 No

how to calculate the neautral earthing conductor size for a 500kva dg set...

Answer / sakthivel

hi mr krl raju sir i want which size of contuctor you
chuse about 350 amp neutral earth comtuctor give full
details

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

One of the advantages of HRC fuse links is that they can be used to back up equipment with an inadequate rupture rating. briefly discuss what this means

1 Answers  


in india ac frequency is 50hz, but in foreign countries it is 60hz,whwt is the reason

9 Answers   SVIT,


is it possible to give the total load from the supply generator's maximum in practical?

2 Answers  


will a transformer work when pulsating dc id applied to its primary?? what will be the result??

2 Answers   cemp,


Instead of single phase(220), if apply Phase to phase supply (eg: for lighting fixture). what will be the power formula? what will be the volt and current value? please explain me with some example.

1 Answers  






what is the advantage of connecting capacitors in delta than in star?

1 Answers   NTPC,


Can a transformer designed for a particular voltage and frequency rating be used for different set of mentioned ratings? Assume that the winding does not get burnt because of overheating at higher voltage. If yes, then under which constraint it is possible?

1 Answers  


what type of earthing do for dry fissure rock?

0 Answers  


DEAR SIR/MADAM,CLEARLY EXPLAIN ABOUT CRAWLING AND COGGING EFFECTS IN INDUCTION MOTOR.

0 Answers  


how can i find ct ratio of meter by seeing name plate of meter and how it should be used in MF calculation if it shows only-/1???

0 Answers   Harshal Electrical,


We use MCCB not MCB for motor starters because MCCBs has capablity to drawout the motor starting current which is 5-6 times the full load current of motor for 1sec. Then why we use SDF in starter panel means MCC panels. Pls reply if any one knows this answer.

1 Answers  


What is the maximum advisable distance where it is required to interconnect a 500 KVA 480 V 3 ph transformer and the main panel or MCC ignoring the voltage droop affectation, does it is exist any standard about it?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)