What is the cause for a blown fuse in one phase of primery
side(HV) of a three phase transformer( 4169v-460v) in the
time of closing its supply breaker.
There is no load on the secondery side of the transformer
in this moment.
Answers were Sorted based on User's Feedback
Answer / engr.abdurrahim
As your Question, I think in your transformer is having
interturn fault or single phasing or may be LG
fault.Without load if any fuse blown means connected things
(Transformer)itself having problem.
Solution:
Do the Meggaring and check insulation between, phases at HV
side,LV side,
Check insulation between phase to neutral, Phase to earth.
Check Earth resistance also.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / pillay
It could be just high inrush current,
incorrect fuse size or a defective fuse
in the first place.If it recurs than
further investigations should be taken.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / niranjan
Due to high inrush of current or there may an inter turn
fault on ther primary side of the transformer
Is This Answer Correct ? | 1 Yes | 2 No |
WHAT IS M.P.C.B
In the Variable Voltage Variable Frequency Drive, how the Voltage and Frequency varied ? Is it varied in the Inverter part of the Drive ? Please give us supporting document if any.
explain impact of tariff on energy management..? and what is ABT tariff
What is substation?
WHY ARMAD USE IN CABLE
Three phase star connected PT transformer primary side one phase fuse is blown what will be the output in secondary side(Secondary side also three phase star connected)
what is the use of earthing ?
why inductivedrop in dc motor neglected
1 HP = how many Kva
any calculation method for decide cable size for current?
132 KV TRFO BUSHING BURNT WHEN A 6.6KV HAS BEEN APPLIED TO IT .WHY .ANY REASON ?
why we ht line cable size small rather than lt cable.