I am having a DG set.The 415 V from Generator is step up to
460 v and then the same is used for Induction furnace.
before Step up, I am connecting LT load to my factory use.
When Induction furnace is in service from DG, when i try to
start a motor, the generator is tripped.Please tell me the
reason.
Answers were Sorted based on User's Feedback
Answer / asif.k64@hotmail.com
Also check if the motor starter is working properly and APFC
panel is off while generator starts, check the fault codes
on the breaker if you have an ACB connected in the AMF panel.
Though there could be many other reasons as well but I would
rather check these things as well.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / r.shanmugasundaram
Induction furnace controller is basically a rectifier cum
Inverter. Generally Rectifiers will generate Harmonics.
Suppose if the DG is not selected to accomodate this non
linear load then the sinusoidal wave form gets distorted
and will trip the DG set or other connected loads which
involves electronic circuitry. May be you can check
with an oscilloscope how the sinusoidal wave pattern
changes when Furnace is switched On. Suppose if the wave
form distortion does not happen then ther could be some
other reason
| Is This Answer Correct ? | 1 Yes | 0 No |
our scope called one core cable for distribution system so we like to use 4 core cable with one equipment grounding conductor so what kind of technical reasons i can say that the 4core is better then 1 core,
Why is earth connected to neutral on transfomer installations
Why the brushes used in dc machines are made of carbon not from other metal?
what is the role of energy meter in distribution system ???? technical and non technical losses in distribution system????
can indirect loading be called as phantom loading?
what is the use of CAPACITOR in CFL lamp?
what mean ohm
how to calculate cable size
why field resistance is higher than armature resistance in dc machines? and why filed resistance is kept at min value at starting in same time of armature resistance at max value?
The control system is used for?
what kinds of Transformer oil grade is better for power transformer ?
Where is the center of magnetic field in alternator
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)