how to select the power contactor in Diffrent AC motors.
Answers were Sorted based on User's Feedback
Answer / navnit bhimani
Motor full load current=H.P.x1.5 in three phase line
Motor full load current=H.P.x4 in single phase line
you can select 20% over size than full load current.
Is This Answer Correct ? | 30 Yes | 8 No |
Answer / prabhu gnanasekaran
All power contactors has to be selected as per the TYPE 2
CO-ORDINATION chart. Which will have the KW rating of the
motor with Line current and starting current. So TYPE 2 CO-
ORDINATION chart will be the base for the selection of
power contactors.
Is This Answer Correct ? | 17 Yes | 5 No |
Answer / sahilsmohan
This is depend of utilization of motor :
A.C motor) A.C 1 to A.C 4 : slightly
inductive,slipring,squirel cage ,starting ,stoping, and
plugging, inching .
DC motor ) DC1 TO DC4 slightly induction, series
/shunt,staring stopping, pluging, inching
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / amit kansara
first of all determine what is the duty type - ac-2/ac-3 /ac-4
accordingly select the right contactor for manufacturers
catalogue.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / pvr.parthasarathi
For selecting a power contactor for a particular motor the following points are to be considered.
1) Type of the motor ie. Squirrel cage, Slipring .
2) Full load of the motor and its Voltage .
3) Operating cycle of the motor ie. S1 , S2 -----.
4) Nature of the drive ie. cycle of operation such as normal , jogging, Breaking etc.
So selecting the contactor for a motor does not have single point formula. But as a thumb rule for 3 phase motors it can be selected at 130 percent of FLC, if all other factors are normal.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pramod
As per the different manufacture the give its selection
chart but techanically calculate the motor full load current
of the motor and select the nearst current size of contactor
as per different manufacture Power Contactor List
Is This Answer Correct ? | 13 Yes | 18 No |
How can we calculate the Rating of DG Set for a 4 kw motor?
what are the range of memory address in plc for L&T lx7 4A
How to take of Transformer oil Break down voltage test?
state basic meaning of 'INDUSTIAL AUTOMATION'?
If Neutral Grounding Resistor (GR) failed/shorted. Is it repairable.
why when i start my diesel generator it takes 1 minute or less then stop, and i checked the oil sensor is ok and when the generator start i can get 220 voltage but it it is stop after 1 minute or less, how can i solve this problem?
In power transformer YnD0 Vector Group is possible or not? if possible, what will be the vector diagram and what are the conditions?
what is the difference between torque induced and torque load?compare them with respect to dc motor?
Why R ph of Hv and Lv is shorted or joined together while taking vector group?
how does a tube light choke working?
Tell me in detail about c.t. And p.t. ?
Excat meaning of burden in only one word?
3 Answers Bhel, DG Electricals,