why it is important to earth neutral of 3 phase transformer?
Answers were Sorted based on User's Feedback
Answer / er. ankush miglani 9718151073
it is done to make the neutral at zero potential
coz if there is unbalance in potential the neutral may
shift.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / guest
when there is a unbalace among the phases due to change in
load circulating current introduced this fault caurrent can
be eathed via neutral .
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / pranjal.job
it is because to make path for the current generated due to imbalance in d three phases
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / srinivas@vsp
for stepdown distribution transformers the secondery side ie
lt side y-with nutrel earhto be connected because of load
side the current is not zero ie varying.hence we r connected
y-with nutrel earh......... finally this because of stand by
earth fault in load sideie secondery side..
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / guest
to provide the protection from the over current,over loading
| Is This Answer Correct ? | 0 Yes | 5 No |
What is maximum power transfer theorem?
When steam condenses and becomes water at the same temperature, the specific heat for the process in kJ/kg k is
why earthing is not required on transformer prymary winding side ???
What is the operational principle of direct current current transformer and direct current potential transformer?if possible plz reply with ckt. diagram.
how will protect transformer agint overcurrent protection
how the calculation is done if the DG set require for the -- -48 to -51v 4000 ah battery set .
What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.
what is the highest transmission voltage in india???
49 Answers Bhel, EIPL, Engineering, Jindal,
What is the formula of frequency ?
What is ignition module of a CAT Gas Genset G-3508 Engine, Alternator SR4B Series. HOw its checked for correct functioning.Is it repiarable or replacable?
I have made a 3 phase thyristor full bridge rectifier. But at the moment it is working only for the half bridge operation. Both the half bridges are on operation separately but when i put it into full bridge operation the oscilloscope output is zero. I rechecked that the pulses are correct for each thyristor. what could be the possible reason for this?
How to Calculate The Neutral Earth flat design calculation for the Synchronised generator (Gen 1-650Kva, Gen 2-725Kva
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)