WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?

Answers were Sorted based on User's Feedback



WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / welcome4ujd

you can use fluke milliampre simulator tocalibrate a
controlvalve through i/p converter, ot by using a druck
pressure calibrator directly to the controlvalve positioner.

Is This Answer Correct ?    30 Yes 1 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / upendrae

we can use the 4-20ma source for calibration of the electro
pneumatic valves.

Is This Answer Correct ?    13 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / tarun

CONTROL VALVE HAVE MOSTLY 3 PART BODY,BONNET AND
ACTUTOR,CONTROL VALVE REQUIRED AIR SUPPLY 20 PSI OR 140KPA
AND SIGNAL 4TO20MA AND TOOLS AND STANDURD P.G OR DRUCK. SO
FINNALY WE USE ENOMET SOURSE, DRUCK, OR REGULATOR AND AIR
SUPPLY REQUIRED

Is This Answer Correct ?    9 Yes 2 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / murugesan

First ensure both I/P and positioner air supply are as
it should be before starting up control valve
calibration/stroke checking activity. Then take any of loop
or multifunction calibrator based on the instrument
availability in your plant for Ex 707Ex, UPS-III-IS, UPS-
II, UPS-IS, DPI610 IS (connect series with 24 VDC supply),
UNOMAT and 725Ex

And select “mA source with 24V DC” option and connect 4-
20mA source to I/P converter and simulate appropriate mA to
check the stroke. Normally control valve stoke checking is
called as control valve calibration.

Is This Answer Correct ?    2 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / rushikesh s gaddpawar

CONTROL VALVE CALIBRATATION MANLY USE MA POWER SUPPLY
SOURSE TO CALIBRATE CONTROL VALVE

Is This Answer Correct ?    0 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / balu

WE CAN CALIBRATE IT THROUGH A MILLI AMPS FEEDER IN PRESENT
DAYS

Is This Answer Correct ?    0 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / ali faozy

if the control valve has i/p &postioner we need [ 4 to 20 ]
milliamper dc source , 140 kpa air supply for i/p and 700
kpa for positioner [depending on positioner supply
recommendation]
we need also to calibrate the strock indicator for fully
open and fully close positions
if the control valve has no i/p & positioner then we need
air signal source of [20 to 100]kpa depens on control valve
design
and 700 kpa air supply for valve supply

Is This Answer Correct ?    0 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / shabbir ahmad mughal

we use loop calibrater and miliampere source for
(pst)partial strok testing or calibration of control valve

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

How to calibrate H2s Dectector

0 Answers   KOC,


send me HPCL paper

6 Answers   HPCL, Shuiba Hotel,


what is dry leg and what is wet leg?

3 Answers  


why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA?

8 Answers   Emerson, IEM,


Are Coils of Electromagnetic flowmeter in direct contact with fluid material

4 Answers   TATA,






Is it possible to drill additional gland hole in EExd or EExe JBs? What are the points to take care?

2 Answers  


How to calibrate and check thermal mass flow meter of Make thermal instrument company inc model 60?

1 Answers   Wood Group,


if we put any thermocouple on a table in a room without any connection,what temperature should it show.

3 Answers  


units for vibration in power plant

1 Answers  


I want to know about DDCMIS in detail ? please explain it. Also give name of reference books in which it is explained in detail in very simple manner.

0 Answers  


If a control valve is hunting means means if we are giving 50% to the cv, the cv will open at 51% then slowly slwoly it will reaches 49% , then it will reaches again 50%, this type of action occured frequntly.. so what to do for solve this problem. The possible cause is in volume booster or positioner's relay.. positioner is double acting .. and make siemens..sipart.The cv is double acting and mounted for anti surge operation, it having 4 nos. volume booster, one sov, one positioner, etc..?

2 Answers   Gujarat Fluorochemicals Limited (GFL), Shell,


how to calculate the temp. of RTD&Thermocouple when we got some mV r Ohms?if anybody has d chart pls mail the chatrs to me...

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)