1)how can calibrate temperature transmitter?
2)how can calibrate flow transmitter?
3)how can calibrate level transmitter?
Answers were Sorted based on User's Feedback
Answer / tontoy
1 prepare the instruments needed in calibrating temp.
transmetter.
2 unsrew the resistance input of the transmetter, and
connect it to a resistance box.
3. unsrew the output side of the transmetter, connect the
ammeter serries with the supply of 24 volts dc.
4. supply it with the resistance of 0% or 100 Ohm until
100%. and record it to the data in the as found.
5. the next is the zeroing. supply the input with 100ohm
resistance. adjust the adjustment of the zero side by
twisting slowly to the left to have an output of 4mA.
6. span- supply the transmitter with 100% depends on the
value of high temperature of the RTD value. and adjust it
to 20mA.
7 repeat it up to 4-5 times.
then supply is again with 100Ohn, mast have an output of
4mA until 100%.
record it to the data as asleft.
for 0% must have an output of 4mA, 25% 8mA, 50% 12mA, 75%
16Ma, and 20mA for 100%.
Is This Answer Correct ? | 101 Yes | 17 No |
Answer / sumit yadav
1)There is equipment available where we can put RTD and
give temperature.Now set temp transmitter parameters to
produce mA equivalent to temp given.
Is This Answer Correct ? | 71 Yes | 26 No |
Answer / gcs
1. First select the calibrating equipment
2. for ex: For RTD, select RTD circuit with zero and span adjustment potentiometers.
3. make the input quantity (temperature) to zero.
4. adjust the zero adjustment pot ntill the output of the RTD becomes zero.
5. make the input quantity to high (Ex.100 deg) and adjust the span pot till the output becomes 100.
6. Repeat steps 3 through 5 till there are no changes in zero and span pot.
7. now the instrument is calibrated.
Is This Answer Correct ? | 13 Yes | 22 No |
can we create an interrupt in plc through scada?
How many input(Analog and digital) and outputs(Analog and digital) are there in DELTA v DCS Version 7.0?
why we use casced loop
What is the syllabus for Instrumentation Engineers, who wish to join the Public Sector Units??
how to replace the smart transmitter software
䑰ҕ䔈ҕ䖠ҕ䘰ҕ䛀ҕ䝐ҕ䟐ҕ䢐ҕ䥐ҕŹ
I have 0.75mm sq multicore cable (IS type) , can use instead of same type but 1.5 sq mm cable ? Note : The distance is around about 150 meter.
what is use of communication wire in multipare cable(oil and gas field), why this communication wire not used in single pair cable?
what is zero trim and span trim?. at which problem we need to use this?
How does one detrmine the direction of movement of core in an LVDT?
What is use of condensate pot
5 Answers Alstom, Petrocil, Samsung,
How would i calibrate a new commissioned flow transmitter???