1)how can calibrate temperature transmitter?
2)how can calibrate flow transmitter?
3)how can calibrate level transmitter?
Answers were Sorted based on User's Feedback
Answer / tontoy
1 prepare the instruments needed in calibrating temp.
transmetter.
2 unsrew the resistance input of the transmetter, and
connect it to a resistance box.
3. unsrew the output side of the transmetter, connect the
ammeter serries with the supply of 24 volts dc.
4. supply it with the resistance of 0% or 100 Ohm until
100%. and record it to the data in the as found.
5. the next is the zeroing. supply the input with 100ohm
resistance. adjust the adjustment of the zero side by
twisting slowly to the left to have an output of 4mA.
6. span- supply the transmitter with 100% depends on the
value of high temperature of the RTD value. and adjust it
to 20mA.
7 repeat it up to 4-5 times.
then supply is again with 100Ohn, mast have an output of
4mA until 100%.
record it to the data as asleft.
for 0% must have an output of 4mA, 25% 8mA, 50% 12mA, 75%
16Ma, and 20mA for 100%.
| Is This Answer Correct ? | 101 Yes | 17 No |
Answer / sumit yadav
1)There is equipment available where we can put RTD and
give temperature.Now set temp transmitter parameters to
produce mA equivalent to temp given.
| Is This Answer Correct ? | 71 Yes | 26 No |
Answer / gcs
1. First select the calibrating equipment
2. for ex: For RTD, select RTD circuit with zero and span adjustment potentiometers.
3. make the input quantity (temperature) to zero.
4. adjust the zero adjustment pot ntill the output of the RTD becomes zero.
5. make the input quantity to high (Ex.100 deg) and adjust the span pot till the output becomes 100.
6. Repeat steps 3 through 5 till there are no changes in zero and span pot.
7. now the instrument is calibrated.
| Is This Answer Correct ? | 13 Yes | 22 No |
Please tell me details about Sox,Nox,SWAS analyser????
what is the meaning of HART ?
How can we use feedback signal frm rtd for monitoring and in dcs for controlling ,then which type of rtd is sutaible 2 , 3,4wire and why ?
what are the documents(Construction point of view for a process plant) submitted by contactor initially entering in to new site for client?
Any body have know try work calculation ???
i am confusing about differential pressure transmitter as i seen so many DPTs in different ranges how can we calculate level and flow with mmh20 plz tel me
compare the thermocouple and pyrometer,which one is the best?why?
what is the input to be given in digital flow meter during the the calibration time?
What is an instrumentation amplifier? How is it better than a differential amplifier when handling outputs from a wheatstone's bridge?
WHAT IS THE Differance b/w on/off & pid control valve?
We are using Rosemount 5400 series Radar Level Transmitters in all types of Sump Applications having oily water hdrocarbon petrochemical nature. What we are facing the problem frequently is that always getting reading frezzed at some value. If we do power recycling , sometimes it is working . then making same freezing problem. If anybody faced before such type of problem and also having solution , Please give the answer.
what is function of switch, and how is it work, explain with difination
0 Answers Bapco Bahrain Petroleum Company,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)